although I have no personal experiance of installing Ground Source I have looked into them.
the biggest problem with them is that if they are not installed or sized correctly, all they will do is freeze the ground they are also installed with big back up immersions to make up any shortfalls.
That is very true - make sure the ground loop is sized sufficiently to meet the demand.
Other usual problems with retrofit install of the heatpumps in the UK:
1. Undersized heat emiters - ideally rads should be 4X the size of the old gas/oil system - warm the house up with 35 degrees flow, instead of 70 degrees when 0 outside.
2. Not enough insulation (to reduce total energy loss, and the required size of the system).
3. Not sufficient education of the end users - they try to use it as their old system, and set it on timer for 2 hours in the morning/evening (instead of using a room stat).
4. Undersized ground loop (Not enoughf land), causing the freezing up...
PS: Why Nobody tries to use excess heat from well sized solar thermal array (like 70-100 vacuum tubes) in the summer to recharge(thaw) the ground loop!? - you just need a couple of valves, pair of pumps and a pair of stats or controller to make it work: have a valve on the flow from the solar heater array going into a plate heat exchanger, going to the return/(pumping station).
Than you need a valve on the flow from the ground loop circuit (with non-return valve before it goes into a heatpump unit), an extra circulator pump, and going into the heat exchanger to cullect the heat from the solar circuit, after returning to the ground loop. Also you need a separate safety cutout, to limit the temperature of the ground loop at 65 degrees, if it uses ethanol as a antifreeze, also make sure the heatpump does not come on when the ground loop circuit is hot, since it can damage it (usually they have limit of max ~30 degrees of temperature on the evaporator side of the circuit).
So the safest bet would be use of pair of the manual lever valves, winter/summer mode, leave ONLY one of them open (+isolate the power to the HP unit when in the summer mode) or to have this functionality (use of the heat from solar colector as a means of thawing/recharging the ground loop) incorporated in the GSHP unit itself by the manufacturers.