halstead ace he 24

  • Thread starter Thread starter gas frank
  • Start date Start date
Status
Not open for further replies.
G

gas frank

Hi guys hope someone can help me out here, i went to this boiler today the ch was not working, the dhw was working fine. checked the thermisters and they are ok. i took a reading from the pcb for the clock and only got 5.6mv it should read 230v, there is 230v going to the clock if that makes since, iam thinking it might be the pcb, any help would be great thanks
 
not worked on one b4, checked my laptop, there can be locking codes whichcan be cleared by powering off for 10 secs. Other than that I would go for the pcb...have u spoke to their technical?
 
Don't be buying pcb's when ur not sure of ur diagnosis, u said ur getting 240v @ the clock? Have u linked the clock out to prove either way, if the pcb is sending power to the clock but the clock isn't sending power back then it's pretty obvious what's at fault. Link out the clock and see what happens, it sounds like the clock to me.
 
not worked on one b4, checked my laptop, there can be locking codes whichcan be cleared by powering off for 10 secs. Other than that I would go for the pcb...have u spoke to their technical?

thanks rory, ya i spoke with the teckie, he suggested it might be lose connection or pcb, there is no code coming up only C on the display,
i checked all the wiring and it seemed to be fine. the pcb is 140 quid
just want to try a make sure before i buy
 
forget halstead techies, rang them last week asking for expected volts off pcb to fan on an Ace he 35, got told, dunno, along with dunno for any other questions, gave up, bought a fan assembly and everything now working. Dont go to service a ace he 35 either, there dont seem to be any burner seals anywhere in the country!!!!!!!!!!!!
 
Don't be buying pcb's when ur not sure of ur diagnosis, u said ur getting 240v @ the clock? Have u linked the clock out to prove either way, if the pcb is sending power to the clock but the clock isn't sending power back then it's pretty obvious what's at fault. Link out the clock and see what happens, it sounds like the clock to me.

yes i linked out the clock and its fine
 
Thing is, if you should be getting 230v and the voltage is 5mV then the pcb just ain't sending it!! You've checked the sensors- ok and i take it all resets have been made, so there are no fuses on the board then there's nowt else but the board. As old plumber said getting pcb's willy nilly isn't always the way, but you've checked all there is.
 
Thing is, if you should be getting 230v and the voltage is 5mV then the pcb just ain't sending it!! You've checked the sensors- ok and i take it all resets have been made, so there are no fuses on the board then there's nowt else but the board. As old plumber said getting pcb's willy nilly isn't always the way, but you've checked all there is.
yes everything else has been checked, i just wanted a second opinion to
make sure, i understand about buying parts willy nilly thats why iam
asking and i appreciate all the help, iam going back to this boiler at the
end of the week and will let you no how i get on, again thanks for the
help.
 
i went back to this job today and replaced the pcb, everything working fine,
again thanks to everyone for there time and input.
 