Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss head breaking device for oil tank? in the Boilers area at Plumbers Forums

Status
Not open for further replies.
B

buchanan90

I need to fit a oil tank 6 meters above the boiler and the manufacturer states if its over 5 meters then a head breaking device needs to be installed yet ive never heard of this. Anybody know what this is?
 
:90:

or
:74:

or
:19:

perhaps?

:banghead:

I've no idea, I'm afraid. Never heard of one.
 
I need to fit a oil tank 6 meters above the boiler and the manufacturer states if its over 5 meters then a head breaking device needs to be installed yet ive never heard of this. Anybody know what this is?

Are you qualified to fit oil tanks?
 
I've always taken a tigerloop as a head breaking device. I maybe wrong but would like to hear everyone's opinions on it.
 
You need one of these, this is from BES:

16394.gif
For use on installations where the ‘head’ of oil is too high for the appliance. Ideal for use on installations of stoves or cookers.
Inlet pressure : 0.5 - 6 bar
Outlet pressure : 100 mbar
Connections : 10 mm x 10 mm compression
Part No.Description Unit PriceQty
16394Oil pressure regulator£20.97

 
Status
Not open for further replies.

Similar plumbing topics

https://www.pipelife.co.uk/content/dam/pipelife...
Replies
6
Views
2K
External hounsfield heat only. If you really...
Replies
4
Views
967
hi, no current pipework in concrete i believe...
Replies
7
Views
1K
Look at a Viessman 222 10 year manufacturers...
Replies
10
Views
2K
Replies
9
Views
936
Back
Top