Was changing 3 rad valves on a combi in a flat. Create a vaccuum to avoid drain down, changed the valves, re-filled and then when I turned off the filling loop noticed the pressur guage kept creeping up. Checked filling loop wasn't passing. Even when detatched and with the house mains off (i was trying everything to reassure myself) it kept creeping up until I let the pressure out again. I phoned tech support (i'm not gas safe, don't know nowt about boilers) for Worcester (was a greenstar junior 24) and they said it meant heat exchanger went. They said it couldn't have been anything I did. Landlord was totally cool about it, I recommended a local gas safe guy to look at it.
My questions are:
1) Was tech support correct?
2) How common is this? I've done this kind of job many hundreds of times and not had it but may have been unusually lucky.
3) How was the pressure going up? Where was the extra water coming from?