Having looked through a number of MIs why do heatpump manufacturers still insist that an external heatpump is acceptible for domestic hot water, its certainly not the way I do it.

So how do you guys keep efficiency to a maximum on your external heatpump and still produce domestic hot water cheaply.
Discuss
 
In my eyes the fact that manufacturers claim that theyre units can do domestic hot water completely goes against EN14511 which is the standard that all manufacturers have to meet to be MCS accredited products, but if they advertise there units as doing domestic hot water this means that their units will always be working out of parameter
 
Just found this on Danfoss web site Q&A about there ashp

Will it provide enough hot water for baths showers & domestic hot water?

With the correct design and equipment, all domestic hot water requirements would be provided by the air source or ground source heat pump throughout the year. Heat pumps produce water at a lower temperature than boiler systems. Instead of water that may be scalding water produced is hot enough for all normal domestic requirements. You will notice that you do not have to add as much cold water to your baths and showers. The aim is to save money and energy with either an air source or ground source system. There is no point in taking water to temperatures that can't be used anyway (above 55°C).



WOW no point in preventing[h=1]Legionella ????????[/h] then
 
I read of one the other day that claimed up to 80° cant remember which one but they didnt mention COP when reaching those temperatures!.. I have always recommended Solar thermal and economy 7 to compliment any heat pump wether its air source or ground source
 
Ecodans heat up to 55oC, but they have an immersion heater built into the tanks in their packaged units to bring the temp up to 65 for legionella prevention. This is usually done on a timer during the night on a cheap rate economy 10 or 7 or whatever.
 
set up the last one fro hw at 50c and use an immersion to top up to 65c at midnight, 10c wont cost a great deal and was included in the running cost per year, have a tmv off the unvented set at 45c so 50c from the heat pump is spot on, heat pump heats a buffer first.
 
Amazing, the fact that heatpumps cost more to run at higher temperatures and yet they are being installed to run at temperatures that make them uneconomical just makes no sence to me especially when the heatpump will already be working hard in the depths of winter, Also in my eyes a heatpump that has been designed with a back immersion heater in it has only been designed to work well in certain parameters to attain EN1411 and therefore should not be an MCS accredited unit.
So you thoughts again
 
I've done a heat pump that goes upto 80 degrees, cracking peice of kit. But if radiators and underfloor heating is sized correctly, and the heat pump is sized correctly, and the correct tarrif is setup on the electric meter then the running cost's will be far lower than lpg or oil. I was speaking to a customer today who i installed a heat pump into there 3 bedroom bungalow, married couple 2 young kids, they have worked out that average heating and hot water bills has been 10 pound a week over the year, and thats with temperatures dropping down to -15 in the winter
 
I've done a heat pump that goes upto 80 degrees, cracking peice of kit. But if radiators and underfloor heating is sized correctly, and the heat pump is sized correctly, and the correct tarrif is setup on the electric meter then the running cost's will be far lower than lpg or oil. I was speaking to a customer today who i installed a heat pump into there 3 bedroom bungalow, married couple 2 young kids, they have worked out that average heating and hot water bills has been 10 pound a week over the year, and thats with temperatures dropping down to -15 in the winter

I assume thats a high temp one then
 
Dakin use an external unit and the second stage heat pump is internal which takes it up to 80c

It uses refrigerant pipe work between the two units

It is supposed to give COP of over 3
 
we've got a nibe 2015 docked to hot water cylinder. 146ltrs hot water, 120 central heating and 20 ltrs solar. The way it has been set up the pump uses the immerser as well as the air source. If we switch the immerser off we get between 50-60 litres of water at 43deg from the air source(tonight). If the sun shines (wot) the solar will take the temp up to about 50-52deg. Nibe say that the f2015 should heat the 146ltrs to around 50+ without the solar or immerser.
We went from 185ltr at 65deg water tank that cost during last years summer, 72p to heat, total daily electric less that £2.00 to this summer over £3.50 daily and inadequate hot water, if we leave the system on auto, thats using immerser and air source. We have never had the heating on during the months May to October but with this system on auto we get warm radiators and on one occasion the house was at 25deg, phew. We are awaiting the installers return visit with trepidation

NIBE F2015 can both heat hot
water effectively at high outdoor temperatures and give a high output
to the heating system at low outdoor temperatures
 
if we leave the system on auto, thats using immerser and air source. We have never had the heating on during the months May to October but with this system on auto we get warm radiators and on one occasion the house was at 25deg, phew. We are awaiting the installers return visit with trepidation


Why are you advertising this company if the system is not working correctly?????
 
we've got a nibe 2015 docked to hot water cylinder. 146ltrs hot water, 120 central heating and 20 ltrs solar. The way it has been set up the pump uses the immerser as well as the air source. If we switch the immerser off we get between 50-60 litres of water at 43deg from the air source(tonight). If the sun shines (wot) the solar will take the temp up to about 50-52deg. Nibe say that the f2015 should heat the 146ltrs to around 50+ without the solar or immerser.
We went from 185ltr at 65deg water tank that cost during last years summer, 72p to heat, total daily electric less that £2.00 to this summer over £3.50 daily and inadequate hot water, if we leave the system on auto, thats using immerser and air source. We have never had the heating on during the months May to October but with this system on auto we get warm radiators and on one occasion the house was at 25deg, phew. We are awaiting the installers return visit with trepidation

NIBE F2015 can both heat hot
water effectively at high outdoor temperatures and give a high output
to the heating system at low outdoor temperatures

So what you are saying is that your installers have installed a heat pump to do your heating and domestic hot water and to do the domestic hot water it is in fact working outside its parameters therefore costing you as a customer more money to run than it should and also that in the winter they are hoping that every day is a sunny day for the solar thermal??
 

Similar plumbing topics

C
  • Question
Thanks for replying matey. You've been a...
Replies
3
Views
1K
They were quite accurate IMO and might look...
Replies
12
Views
1K
A
  • Question
We have low hot water pressure in the entire...
Replies
0
Views
530
Abram R
A
  • Question
I don't know if you are aware of the "Society...
Replies
8
Views
1K
  • Question
OK, here's some info I found. It seems that...
Replies
1
Views
1K
Back
Top