A
Adam85
Hi, I'm a proffesional gas safe plumbing & heating contractor with over 10 years experience, about 4 months ago I had a problem with the hot water flowing hot and cold on a Heatline c24. With the hot tap on fully you can see the burner go to full flame for about 20seconds then drop down to min flame for a couple seconds then shoot back to full flame, hence the water temp rising and falling. I changed the h/w ntc sensor and that solved the problem for about a week then the same problem but instead of the flame dropping to minimum it would shut off then re-light within a couple seconds. I had a spare new pcb, fitted that still no different so changed the hot water heat exchanger which was partially blocked with black iron oxide deposite. Fitted a magna clean on return to boiler, flushed system re-filled with inhibitor and all was fine for the last 4 months now it's doing the same thing again, I checked the magna filter and there were small deposits nothing to shout about, I'm baffled surely the plated heat exchanger can't be blocked again and the ntc is only 4months old. Any help would greatly appreciated.