Hobo128 Gas Engineer Messages 292 Apr 27, 2017 #1 Any help with this rubbish boiler would be helpful. Open hot tap and water is only warm. Display says 30c . Changed diverter cartridge but no good, check plate heat which seems fine.
Any help with this rubbish boiler would be helpful. Open hot tap and water is only warm. Display says 30c . Changed diverter cartridge but no good, check plate heat which seems fine.
ShaunCorbs Super Moderator Staff member S. Mod Plumber Gas Engineer Subscribed Messages 34,719 Solutions 1 Apr 27, 2017 #2 Does it fire when hot tap is opened ? Upvote 0 Downvote
Hobo128 Gas Engineer Messages 292 Apr 27, 2017 #3 ShaunCorbs said: Does it fire when hot tap is opened ? Click to expand... It does fire, it does not modulate down either Upvote 0 Downvote
ShaunCorbs said: Does it fire when hot tap is opened ? Click to expand... It does fire, it does not modulate down either
ShaunCorbs Super Moderator Staff member S. Mod Plumber Gas Engineer Subscribed Messages 34,719 Solutions 1 Apr 27, 2017 #4 Have you checked temp sensor ristance ? Upvote 0 Downvote
jtsplumbing Esteemed Plumber Gas Engineer Subscribed Messages 5,728 Apr 27, 2017 #5 Sounds like its not going onto full burn, PCB or Gas valve maybe ?? Upvote 0 Downvote
townfanjon Esteemed Plumber Gas Engineer Subscribed Messages 8,627 Apr 27, 2017 #6 Hw thermistor maybe . What temp diff have you going in and out of the plate Upvote 0 Downvote