Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss HELP - Back to back WC's issue with cross flow in the UK Plumbers Forums area at Plumbers Forums

Messages
4
Morning all,

Struggling to resolve a problem. Back to back WC's in a fourth floor flat and the waste from toilet A(main bathroom) transfers into toilet B (ensuite) we have installed the McAlpine ARB 1 anti-cross flow valve on each side but it has only stopped solids and there is still some fluid getting through.

I have attached images of how this looks. How would you advise we fix this?

Appreciate any advice.

Many thanks,
Jack
 

Attachments

  • ensuite 1.jpg
    ensuite 1.jpg
    118.5 KB · Views: 47
  • ensuite pipe connection to main.jpg
    ensuite pipe connection to main.jpg
    168.1 KB · Views: 42
  • main 2.jpg
    main 2.jpg
    67.3 KB · Views: 39
  • main stack pipe.jpg
    main stack pipe.jpg
    110.9 KB · Views: 39
  • main.jpg
    main.jpg
    71.9 KB · Views: 39
Sorry to say not easily. Both outlets would ideally drop in a near horizontal float to the stack. It was refreshing to see he has used a 45 branch but it is so close to connecting we you are asking for problems. Not straight forward to recover from.
 
If you can, lower the branch on the stack - but it looks as though you can’t.

If you can’t lower it.

Change the branch to a double corner branch and run each wc separately back to it (this is one where the two branches are at 90 degrees instead of the more usual 180.

I’m assuming as it’s a flat you can’t drop one of them through the floor and connect to the stack lower down - you could if the services all run in a common, accessible cupboard as they sometimes do......
 
Especially given the 45 branch and it's distance from the ensuite pan, I'd say there's a partial blockage in the branch pipe (with the white collar) or in the stack if there are no flats higher.

There would have to be quite a build up to get fluids to flow back to the Ensuite pan.
I think I'd cut a rodding eye into the branch near the stack junction to watch the water flow when flushed.
It may be usefull in the future if there's any blockages.
 
I think you could well be right as assuming the toilets were not going to be put elsewhere, the plumber has done the right thing and the best they can given the setup. I would have not expected any noticeable cross flow looking at how it's been connected up.
 
uming the toilets were not going to be put elsewhere, the plumber has done the right thing and the best they can given the setup. I would have not ex
If you can, lower the branch on the stack - but it looks as though you can’t.

If you can’t lower it.

Change the branch to a double corner branch and run each wc separately back to it (this is one where the two branches are at 90 degrees instead of the more usual 180.

I’m assuming as it’s a flat you can’t drop one of them through the floor and connect to the stack lower down - you could if the services all run in a common, accessible cupboard as they sometimes do....

Do you mean like this one? Seems a good idea! hmmm
 

Attachments

  • Capture.PNG
    Capture.PNG
    72 KB · Views: 20

Similar plumbing topics

  • Question
You need a mcalpine V33WM, the site won't let...
Replies
7
Views
666
  • Question
Morning Ben-gee Again, many thanks for...
Replies
5
Views
1K
    • Like
From this post, I think you’ve got a good...
2
Replies
47
Views
5K
  • Question
Yes, The size of the external expansion...
Replies
17
Views
10K
Back
Top