professorplumb
I serviced a boiler the otherday and they client then asked me to look at their business boiler as not worked for about 6 months. She said she had a guy look at it but said wasn't sure and never seen again.
I am wishing i had done the same.
The boiler is a baxi system 100HE plus. when i arrived it would ignite and stop within 3-4 secs of lighting. It would try this a few times then go to lockout.
I said it requires a good service as the trap is blocked, seals around the combustion cover are part damaged and the HEX is full of s***te. She then told me it had not been serviced since installed about 5 years ago.
So i serviced the boiler before cleaning the Hex i noticed it was leaking so i upped the pressure and sure enough the heat exchanger was in need of replacing in which i replaced.
I now try and start the boiler and i get the stop start lighting of the burner. I cleaned the probes and that seemed to have done the trick. I checked the gas supply in and thats fine at 18.5mb. I then fired it up and it works with it being lit for about 1.5 mins the flame seems really large and the panel very hot. MI says to wait 3 mins before gas rating i'm a bit scared to leave it this long.
Can anyone give me some pointers as paid out about £300 thinking i could fix it.
Its getting to the point where i am contemplating gatting in Baxi for them to resolve.
thanks in advance
Simon
.................................................................................................
Update.
I have spoken to Baxi whom asked me to check 240v to gas valve (their was), Ohms of 4.3 (their was) not sure what the ohms things was all about. I fired the boiler up although it took a while to stay alight which may be the flame rectification probes and spark . Boiler stayed on for aprox 15 mins. temp on the flow got to about 50 degrees before tripping out. i assume it was the stat on the fan.
The flame seemed way to high as was lifting the ceramic burner plate ever so slightly. I was also getting readings of 569ppm CO from the flue test point. After it tripped out i looked at the heat exchanger and the new seals at the bottom had cooked.
I think the boiler is burning to rich resulting in high temp and melting the seals and then tripping out the fan stat.
so whats Next.
The fan sucks the gas through which is controlled via the PCB. SO is it the Gas valve, Fan or PCB ???
Simon
I am wishing i had done the same.
The boiler is a baxi system 100HE plus. when i arrived it would ignite and stop within 3-4 secs of lighting. It would try this a few times then go to lockout.
I said it requires a good service as the trap is blocked, seals around the combustion cover are part damaged and the HEX is full of s***te. She then told me it had not been serviced since installed about 5 years ago.
So i serviced the boiler before cleaning the Hex i noticed it was leaking so i upped the pressure and sure enough the heat exchanger was in need of replacing in which i replaced.
I now try and start the boiler and i get the stop start lighting of the burner. I cleaned the probes and that seemed to have done the trick. I checked the gas supply in and thats fine at 18.5mb. I then fired it up and it works with it being lit for about 1.5 mins the flame seems really large and the panel very hot. MI says to wait 3 mins before gas rating i'm a bit scared to leave it this long.
Can anyone give me some pointers as paid out about £300 thinking i could fix it.
Its getting to the point where i am contemplating gatting in Baxi for them to resolve.
thanks in advance
Simon
.................................................................................................
Update.
I have spoken to Baxi whom asked me to check 240v to gas valve (their was), Ohms of 4.3 (their was) not sure what the ohms things was all about. I fired the boiler up although it took a while to stay alight which may be the flame rectification probes and spark . Boiler stayed on for aprox 15 mins. temp on the flow got to about 50 degrees before tripping out. i assume it was the stat on the fan.
The flame seemed way to high as was lifting the ceramic burner plate ever so slightly. I was also getting readings of 569ppm CO from the flue test point. After it tripped out i looked at the heat exchanger and the new seals at the bottom had cooked.
I think the boiler is burning to rich resulting in high temp and melting the seals and then tripping out the fan stat.
so whats Next.
The fan sucks the gas through which is controlled via the PCB. SO is it the Gas valve, Fan or PCB ???
Simon