Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Help from a break down guru with potterton kingfisher mf 80 in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

clemda1

Gas Engineer
Messages
44
hia guys,

Called out to a king fisher this evening hoping someone can help.

Problem:
Boiler not firing.

On arrival found redlight on reset called for heat. Fan engaged but no ignition. Took cover off tested for 240v between live and switch - ok. Called for heat again fan and pump engaged boiler fired nice blue flame for 10 mins.
Put cover back on, retested but again no ignition however fan still running. Pried cover open slightly then boiler fires and stayed on.
I'm think it's an air flow issue but looking for advise as to how to narrow it down.
Venturi or APS or Fan?

Thanks in advance for your assistance
 
will it run with the cover off if yes you have a blockage in the air side of the flue
 
will it run with the cover off if yes you have a blockage in the air side of the flue
hia shaun,

thanks for the reply,
yes it only runs with the cover off. can you be a little more specific regarding where the blockage may be... it's an open vented system so when you say air side of the flu do you mean the inlet via venturi? or inlet vents at the top of the boiler where the flu is? sorry new to this fault finding malarky and this is the first open vented system ive worked on...
 
Are these the ones with the flue stat?
had a look at the manual cant see a flue stat but there is a ttb stat/interuptor.. but i think these detect incomplete combustion...given it runs fine with the cover off dont think this would be the cause
 
hia shaun,

thanks for the reply,
yes it only runs with the cover off. can you be a little more specific regarding where the blockage may be... it's an open vented system so when you say air side of the flu do you mean the inlet via venturi? or inlet vents at the top of the boiler where the flu is? sorry new to this fault finding malarky and this is the first open vented system ive worked on...

Flue, check the air side of the flue is clear then move to other things like fan rpm etc
 
Clean the Venturi on the fan, check flue integrity, check fan blades are clean, check fan speed, test APS.
 
Fan running slow, venturi blocked, APS is failing or an air supply problem with the flue.
 
Clean Fan Blades and venturi - tiny barnacle like residue will stop operation socarbon strips are good for this. Ensure fan turns smoothly. Check APS tubes for wear/ cracks. Heat exchanger clear? If all well and it fails it'll be APS.
 
Status
Not open for further replies.

Similar plumbing topics

P
  • Locked
You need to be a gsr to work on all aspects of...
Replies
3
Views
3K
Dotty
D
  • Locked
No problem when I had my First one of them I...
Replies
20
Views
433
  • Locked
Top Man you avoided that nicely lol I use to...
Replies
5
Views
3K
gasmarc
G
3
  • Locked
Re: Asbestos - Potterton Suprema 80L boiler...
Replies
3
Views
13K
365drills
3
Back
Top