Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Help - potterton powermax HE boiler problems in the Boilers area at Plumbers Forums

Status
Not open for further replies.
S

Steve100

Anyone know how to stop the pressure from going up and then going to lock out on this potterton powermax HE boiler? It has a error message of E 0.1

Any suggestions grateful.

The pressure gauge cuts out at 4.
 
Last edited by a moderator:
filling loop valve is passing, pressure is too high, should be 1 bar when cold, drop system pressure, boiler should fire, check filling loop valve and check valve.
next check the expansion vessel, has not de-pressurized or split, if de-pressurized top up to 1 bar, if split either change or install a separate vessel on the system pipe-work
 
Last edited by a moderator:
Status
Not open for further replies.

Similar plumbing topics

Thank you for the detailed and considered...
Replies
14
Views
1K
J
I've seen a few with boxed in flues and they...
Replies
3
Views
1K
J
Boiler broken down, pay for BG cover, can't...
Replies
2
Views
916
Hello, I have a job with a Potterton Powermax...
Replies
0
Views
864
P
Tricky situation for you. Boiler shouldn't...
Replies
2
Views
473
Back
Top