Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Hi I have slow rising pressure in boiler in the Boilers area at Plumbers Forums

Messages
4
Hi I have slow rising of pressure in boiler not sure why but blue valve its fully open and black one closed..read on web that both should be closed is that true? Trying to attach pictures
 
Is it a combi or just system boiler. Both filling valves should be closed.
If the pressure is creeping it could be a valve letting by. You could have an expansion vessel problem if its creeping when boiler is on. If its a combi it could be the PHX.
 
Hi its combi boiler ideal mini c24 just been told blue one valve should be like that on other forum... was advised to remove silver hose thats what i did pressure dropped by 1/10 bar.. and still now.. looks like valves are ok no leak
 
There should be two valves on the filling loop and a double check valve. Both valves should be in off position once filled.
Yes removing the filling loop to see if either of the valves is passing is one check. If you've done this and there is no leak then that tells me the problem is elsewhere.
Is the pressure creeping all the time or when the burner is running?
 
Your blue one is fine, you have a single tap operated filling valve, the other is your double check valve, hance no water coming out, which you have disconnected. Provided this isn’t passing, I’m guessing you have an expansion issue or a pinholed plate heat exchanger.
 
Last edited by a moderator:

Similar plumbing topics

You might have a EV (expansion vessel)...
Replies
7
Views
496
Hi, I am trying to increase the pressure in...
Replies
0
Views
519
Worked a charm, thanks a lot Shaun!
Replies
6
Views
1K
Hello everyone, Baxi Ecoblue System boiler...
Replies
0
Views
498
I’ve checked the tank as much as I can and I...
Replies
8
Views
1K
Back
Top