Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss High limit stat tripping on a warmflow oil boiler in the Boilers area at Plumbers Forums

Messages
62
Good evening, about 2 years ago a customers high limit stat was tripping every so ofte,n not a sealed system. I turned the circulating pump speed up to 3 from 2 and seemed to cure it , until recently. Tripping again and hes now saying when he turned the Boiler on didn't heat water but rads were hotter than normal. I service and repair oil boilers and have replaced pumps, motorized valves etc many times but I'm not a plumber with a plumbers knowledge. Originally I thought pump for sure, possibly the boiler stat but now I'm thinking motorized valve also, and maybe more than 1 of them. 1 last thing, warmflow boilers have their own stat, I have changed imit stat like for like, is it ok to change a warmflow stat with a imit stat, no point in stocking everything, many thanks.
 
Warmflow boilers used Imit stats for decades, but now use a different (French made I think) stat which I find gives trouble.
The control stat is almost certainly faulty and probably boiler is running too hot and close to limit stat cut off temperature. Less likely to be the limit stat.
You need to replace the entire stat. The pocket is slightly different and although it could still do an Imit stat, you might want to replace everything, or just buy an identical replacement stat to make life easy for yourself.
I have a customer on texting with identical problem on a Warmflow as I type this. :)
 
Warmflow boilers used Imit stats for decades, but now use a different (French made I think) stat which I find gives trouble.
The control stat is almost certainly faulty and probably boiler is running too hot and close to limit stat cut off temperature. Less likely to be the limit stat.
You need to replace the entire stat. The pocket is slightly different and although it could still do an Imit stat, you might want to replace everything, or just buy an identical replacement stat to make life easy for yourself.
I have a customer on texting with identical problem on a Warmflow as I type this. :)
 
Ye I'm told the Boiler is probably kettling ,ye I know what you mean Best about the stats, years ago I've saw warmflow boilers with imit stats fitted, but now seems to be their own. Just a hassle having to stock or go get a warmflow stat, if things were kept more universal, be easier all round.
 

Similar plumbing topics

I once had a similar experience with my old...
Replies
6
Views
856
All sorted now and running better than ever...
Replies
3
Views
1K
Will try to upload pic again
Replies
4
Views
905
I would agree, but only if the high stat were...
Replies
4
Views
1K
hi, no current pipework in concrete i believe...
Replies
7
Views
1K
Back
Top