Hi there, I am about 1st fix 3 x 1 bedroom flats, small 15 litre water heaters under basins and sinks. Electric showers. Problem is there is One 25mm (poly) cold feed with low pressure. Without involving Council for Larger supply to property is it possible to install a suitable pump (booster) to increase a steady flow rate or will this just increase pressure????? And if so any type of boosters recommended? Cheers
 
Hi there, I am about 1st fix 3 x 1 bedroom flats, small 15 litre water heaters under basins and sinks. Electric showers. Problem is there is One 25mm (poly) cold feed with low pressure. Without involving Council for Larger supply to property is it possible to install a suitable pump (booster) to increase a steady flow rate or will this just increase pressure????? And if so any type of boosters recommended? Cheers
Have you calculated the gross water volume when all 3 lecky showers are running ? If they are cheap showers you might just get away with it...are they these one bedroom kitchen/lounge jobs ?
because the ones I survey are only used to sleep in. Anyway
who did the specification if it was not you carry on blame the
Architect We do ! centralheatking
 
Have you calculated the gross water volume when all 3 lecky showers are running ? If they are cheap showers you might just get away with it...are they these one bedroom kitchen/lounge jobs ?
because the ones I survey are only used to sleep in. Anyway
who did the specification if it was not you carry on blame the
Architect We do ! centralheatking
Yeah, there's no specification or Architect.
Yeah, there's no specification or Architect.
Existing main is 23 litres per minute and showers use 6 litres per minute.
 
Existing main is 23 litres per minute and showers use 6 litres per minute.

Six lpm is a low-consumption shower (electric or good quality eco head) but occupants may want to install something a bit more luxurious/wasteful, in which case that number could double or triple.

IMO, a 25mm service pipe is small for three separate dwellings. If you want see whether you can get away with it, you may want to consider sizing the internal distribution pipework to anticipate the possibility of a future upgrade to a 32 or 50mm service pipe.
 

Similar plumbing topics

Cheers, I'll keep at him to uograde, I rekon...
Replies
11
Views
1K
  • Question
Probably all off one main hence your problem...
Replies
3
Views
874
  • Question
Sounds to me that the 15mm pipe that you are...
Replies
14
Views
1K
Essaboy
E
  • Question
You'd need to seek advice from a competent...
Replies
9
Views
2K
  • Question
Something to consider, you maybe able to mile...
Replies
6
Views
2K
Back
Top