I have been to a worcester highflow 400 electronic today which has a problem with hot water. Heating works fine.
Pump starts boiler fires up runs for about 20 secs burner goes off for 20 secs and keeps going like that ( Its got to be a circulation problem) and the radiators start to get warm.
Pump is fine removed diverter all working fine but alot of muck in the system cleaned out a small tube running between DV and the return to the pump. Started looking at the plate but it looks a pig to get out ( Have to remove the flow and return manifolds) and because it was 7.00 and I didnt have any O rings thought it best to leave alone.
Is there an easier way to remove the plate from these boilers without having to remove the flow and return manifolds?
Is there any thing in the flow and return manifolds like Non return valve etc that I should check?
I am pretty certain that its the plate clogged up but could there be anything else I have over looked?
And finally can these boilers be chemically power flushed as that is what it really needs but the last engineer said you cant flush them for some reason and the woman wont listen to me when I say you can. (But I know there are a couple of boilers which didnt react well to cleaner being put in vaillant 828 I think was 1 of them as it swelled the balls in the diverters but they then changed the material of the balls)
Pump starts boiler fires up runs for about 20 secs burner goes off for 20 secs and keeps going like that ( Its got to be a circulation problem) and the radiators start to get warm.
Pump is fine removed diverter all working fine but alot of muck in the system cleaned out a small tube running between DV and the return to the pump. Started looking at the plate but it looks a pig to get out ( Have to remove the flow and return manifolds) and because it was 7.00 and I didnt have any O rings thought it best to leave alone.
Is there an easier way to remove the plate from these boilers without having to remove the flow and return manifolds?
Is there any thing in the flow and return manifolds like Non return valve etc that I should check?
I am pretty certain that its the plate clogged up but could there be anything else I have over looked?
And finally can these boilers be chemically power flushed as that is what it really needs but the last engineer said you cant flush them for some reason and the woman wont listen to me when I say you can. (But I know there are a couple of boilers which didnt react well to cleaner being put in vaillant 828 I think was 1 of them as it swelled the balls in the diverters but they then changed the material of the balls)