Hive wiring advice. | Central Heating Forum | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Hive wiring advice. in the Central Heating Forum area at Plumbers Forums

Messages
4
I recently purchased a hive active heating. I currently have a Honeywell cm900 thermostat wired to my Worcester boiler. I'm just looking for advice as to how to wire the hive receiver which has the live, neutral, earth and 1,2,3,4. Please see pic of the Honeywell receiver. Just to add, there is an isolator switch at the side of the receiver.
IMG_20211002_090043.jpg
 
That’s unusual, I’m wondering if the second L is connected to A at some point? The 2 switching wires are Grey to Common (1 on Hive) and Black to NO (3 on Hive). L and N are straightforward and you can leave earth as is or park in Hive.

Do you have any test equipment?
 
That’s unusual, I’m wondering if the second L is connected to A at some point? The 2 switching wires are Grey to Common (1 on Hive) and Black to NO (3 on Hive). L and N are straightforward and you can leave earth as is or park in Hive.

Do you have any test equipment?
Thank you for your reply.
So I'm assuming that one L is coming from the boiler and the other from the isolator switch, both of these go in the L on the hive?
No I don't really have any testing equipment. Never needed but think I will do now owning my own house.
 
I’m guessing they’ve passed the boiler live neutral through as well from the isolator

So you should have a 3 core cable and a 5 core cable in there

So lives, neutrals and earth in the nest same as old

A -2 on the nest
B-3 on the nest
 
I’m guessing they’ve passed the boiler live neutral through as well from the isolator

So you should have a 3 core cable and a 5 core cable in there

So lives, neutrals and earth in the nest same as old

A -2 on the nest
B-3 on the nest
Yes three wire from the isolator and five coming from the boiler.
I noticed you mention nest but this is a hive, not sure if that makes a difference?
Number 2 on the hive is heating on, number 3 is heating off. So is nothing connected to common? I only ask as I was told to connect to 1and 3.
 
Yes three wire from the isolator and five coming from the boiler.
I noticed you mention nest but this is a hive, not sure if that makes a difference?
Number 2 on the hive is heating on, number 3 is heating off. So is nothing connected to common? I only ask as I was told to connect to 1and 3.

Sorry yes

A-1
B-3
 
Thanks for everyone's help. Hive is installed and working. Only thing I want to do now is extend the wire from the isolator and reduce the conduit to give more wire, all which I'll do when I buy cable. I just find the wiring a little tight due to the Honeywell having cable access via the sides but the hive is only from the bottom. Thanks again.
 

Similar plumbing topics

Hi, I am trying to link a Hive heating & hot...
Replies
0
Views
645
Brilliant. All up and running. Thanks for...
Replies
2
Views
1K
Thanks Shaun I will have a go at it on...
Replies
14
Views
2K
  • Question
Great cheers 👍🏻
Replies
4
Views
836
Back
Top