Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Honeywell Lyric T6 Installation Help in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
15
Hi,

I bought a Lyric T6 to replace my old Potterton EP1 programmer. I've done some research into how it should be wired up however, I'm not 100% sure I've got my wiring diagram correct. As it stands with the current Potterton Programmer we have a constant live feed for the hot water (tap turned on boiler fires) and a timed control for the central heating. I know the saying goes "if in doubt call a professional" but if it's as simple as swapping over the units, ideal! Providing my wiring diagram is correct.

Is anybody able to have a look and offer some advice?

We have a Grant Vortex Pro External Combi 26e boiler with a Potterton EP1 Programmer.

Potterton EP1
img_20171202_120510-jpg.32439

My wiring diagram
lyric-jpg.32440


Lyric Relay Box
img_20171227_171715_01-jpg.32441


Thanks
Doug

IMG_20171202_120510.jpg


Lyric.jpg


IMG_20171227_171715_01.jpg
 
Last edited:
Looks about right

4 is your switched lived
 
There is normally a thermostat between boiler terminal 4 and EP1 terminal 4. You don't show one. Where do you intend locating the Relay box?

Your wiring for the Lyric is basically correct; but I'm not sure about the main feed (on the right), which appears to show Live and Neutral both connected to the N terminal. It won't work like that! ;)

Combi boilers are normally not timed for the hot water as it only runs on demand, and is controlled by a flow switch in the boiler.
 
There is normally a thermostat between boiler terminal 4 and EP1 terminal 4. You don't show one. Where do you intend locating the Relay box?

Your wiring for the Lyric is basically correct; but I'm not sure about the main feed (on the right), which appears to show Live and Neutral both connected to the N terminal. It won't work like that! ;)

Combi boilers are normally not timed for the hot water as it only runs on demand, and is controlled by a flow switch in the boiler.

When I called Grant they said the boiler I have is a condensing boiler and uses a dial on the boiler to adjust the temp from 85c to 65c to keep at optimal condensing temp. the relay box will go where the older EP1 is.

Opps, That's a formatting problem when I saved it as an image and only noticed it when you said. Live connects to L and Neutral connects to N.
Thanks for the reply
 
Last edited:
When I called Grant they said the boiler I have is a condensing boiler and uses a dial on the boiler to adjust the temp from 85c to 65c to keep at optimal condensing temp. the relay box will go where the older EP1 is.
I wasn't talking about the boiler thermostat, which controls the temperature of the water circulating through the radiators, but about a wall mounted thermostat, which controls the room temperature. Am I correct in thinking that you don't have one, which is why you have decided to install the Lyric?

Installing the Lyric relay in the same place as the EP1 is sensible, but you need to check that you have good wireless communication between the Lyric controller and the relay.

The person you spoke to from Grant is only partially correct when saying the boiler thermostat controls the optimum condensing temperature. Condensing only starts to happen if the return temperature (water entering the boiler) is below 55C, and increases as the return temperature reduces.
 
I wasn't talking about the boiler thermostat, which controls the temperature of the water circulating through the radiators, but about a wall mounted thermostat, which controls the room temperature. Am I correct in thinking that you don't have one, which is why you have decided to install the Lyric?

Installing the Lyric relay in the same place as the EP1 is sensible, but you need to check that you have good wireless communication between the Lyric controller and the relay.

The person you spoke to from Grant is only partially correct when saying the boiler thermostat controls the optimum condensing temperature. Condensing only starts to happen if the return temperature (water entering the boiler) is below 55C, and increases as the return temperature reduces.

Thanks. I went for the wired version. No we don't have a thermostat only the EP1 I'm in the process of running the cable that connects the lyric wall unit back to where the relay box will go.
 
thanks for coming back and updating us
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
Here's an attachment of the PDF if people are...
Replies
1
Views
3K
R
  • Locked
Hey all, apologies for the long post: I've...
Replies
0
Views
4K
richardc1983
R
I'm going replace my Honeywell ST9400C and...
Replies
0
Views
2K
Back
Top