Hello Im after some help with a honeywell sundial wiring center. The boiler and pump are permanently on. The cylinder stat was wired incorrectly by the home owner with the common and 2 wires the wrong way round. Having corrected that I am getting 170 volts down the common and 1 wire of the cylinder stat, also down the hw on wire of the programmer. Subsequently also getting 170v down the swl to boiler and orange wire of the danfoss mid position valve.
My thoughts were that the wiring center and lack of relays was causing stray current (don't want to buy new one until I'm more confident with diagnoses). Could the cylinder stat being wired incorrectly have caused this or is the stat faulty?