Hi, I am having to replace the powerhead of a Honeywell 22mm Motorised valve, model is a

Honeywell V4043H1056 (272848)​

it is not that expensive retailing at approx £72 but Corgi do one for £42, is the Honeywell worth the money, the one I have has lasted less than 10 years!

Thanks
Andy
 
Anything more than five years is quite good going for such valves in my experience. If you keep your eye on the market you can sometimes pick up complete Honeywell valves at a very good price.

Some systems give motorised valves a fairly hard life. E.g., if you have a thermostat that uses TPI control the valves may be cycled on-off six times an hour, say 50 times a day for, maybe 100 days a year, i.e. 5000 cycles. So, five years use is 25,000 cycles. Weather compensated systems, if they are correctly set up, cycle less frequently hence less wear and tear.

Whether it's worth trying cheaper parts probably depends on how much the labour to swap them costs you.

Check the valve operates smoothly with the head off. If it's seizing up any new motor won't last long.
 
Upvote 0
Anything more than five years is quite good going for such valves in my experience. If you keep your eye on the market you can sometimes pick up complete Honeywell valves at a very good price.

Some systems give motorised valves a fairly hard life. E.g., if you have a thermostat that uses TPI control the valves may be cycled on-off six times an hour, say 50 times a day for, maybe 100 days a year, i.e. 5000 cycles. So, five years use is 25,000 cycles. Weather compensated systems, if they are correctly set up, cycle less frequently hence less wear and tear.

Whether it's worth trying cheaper parts probably depends on how much the labour to swap them costs you.

Check the valve operates smoothly with the head off. If it's seizing up any new motor won't last long.
Thanks very much, I will be fitting so no labour costs. The valve controls the flow to the upstairs radiators when it is working, I had not noticed it had failed until the pump tripped due to too much workload being placed on the immersion heater that was the default! I will maybe replace the whole valve rather than the powerhead?
 
Upvote 0

Similar plumbing topics

  • Question
Yep, here mentions rebinding.
Replies
9
Views
5K
Deleted member 120897
D
true, according to the documentation it...
Replies
3
Views
1K
  • Question
Thank you so much. I am now officially out of...
Replies
22
Views
3K
Back
Top