Hello I have checked for items on this forum for problems with honeywell valves but didnt find any that related to a problem I have.
I am not a plumber I am a control systems qualified technician.
The problem I have is both with honeywell whos support is very poor. In not returning phone calls and what I think is the poor design of their zone valves.
Now they are a very cheap motorised valve but they should still work!
The basic problem with them seems to be that to open the valve it has to be energised, simples as the meercat says. I have had 3 of them burn out due I would suspect to being continually on for say 5 hours at a time. ( the motor is energised continually even though not turning whilst the valve is valve is called to open).
In order to (help) with this problem I used a change over micro switch on the end of the valve travel to switch a diode into the circuit, so that at the end of travel the motor supply is switched through the diode to reduce the power by half to the motor. By some strange trick of feat that motor did last twice as long as the first 2. It still burnt out eventually however.
Honeywell completely deny that this is happening with their valves I dont believe them. I also know that ASCO do make a valve that is sequential with a signal but they are expensive and are on /off very fast opening which is not as good for the system as the gradual opening of the honeywell. I was wondering if anyone else has had burn out problems with this honeywell, or that I am doing something stupid like by fitting a diode reducing the frequency of the applied voltage thereby reducing the Xl and actually increasing the power to the motor. Or am I talking rubbish as theres nothing wrong with the things.
I am not a plumber I am a control systems qualified technician.
The problem I have is both with honeywell whos support is very poor. In not returning phone calls and what I think is the poor design of their zone valves.
Now they are a very cheap motorised valve but they should still work!
The basic problem with them seems to be that to open the valve it has to be energised, simples as the meercat says. I have had 3 of them burn out due I would suspect to being continually on for say 5 hours at a time. ( the motor is energised continually even though not turning whilst the valve is valve is called to open).
In order to (help) with this problem I used a change over micro switch on the end of the valve travel to switch a diode into the circuit, so that at the end of travel the motor supply is switched through the diode to reduce the power by half to the motor. By some strange trick of feat that motor did last twice as long as the first 2. It still burnt out eventually however.
Honeywell completely deny that this is happening with their valves I dont believe them. I also know that ASCO do make a valve that is sequential with a signal but they are expensive and are on /off very fast opening which is not as good for the system as the gradual opening of the honeywell. I was wondering if anyone else has had burn out problems with this honeywell, or that I am doing something stupid like by fitting a diode reducing the frequency of the applied voltage thereby reducing the Xl and actually increasing the power to the motor. Or am I talking rubbish as theres nothing wrong with the things.