Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Horizontal hot water cylinder install. Does this look correct? in the UK Plumbers Forums area at Plumbers Forums

Messages
1
Can anyone assist me? I don’t know much about plumbing so got a plumber in to install this for us, however I’m not sure if it looks correct, there are wires going behind hot water pipes, and a lot of the pipes look to long or too short which in turn appears to be causing strain on other parts.
Anyone out there able to help? Is this correct or are there things wrong and if so what?
 

Attachments

  • 0DF3E755-B557-4E8F-8C43-755D608150BC.jpeg
    0DF3E755-B557-4E8F-8C43-755D608150BC.jpeg
    656.8 KB · Views: 43
  • 2EBD252A-1A8B-4E75-A351-9A3D8F9513AE.jpeg
    2EBD252A-1A8B-4E75-A351-9A3D8F9513AE.jpeg
    664.5 KB · Views: 36
  • 49620C57-1F1C-42C5-BF60-150547BB3D30.jpeg
    49620C57-1F1C-42C5-BF60-150547BB3D30.jpeg
    281.2 KB · Views: 35
No couple of items

All the pipes need lagging / insulating
D2 is incorrect Material (the white plastic waste pipe)
Can’t remove immersions for maintenance/ replacement
Also have you had building regs certification ?
 
Looks a rough job.

No 300mm under discharge (Depends if you're including trap which I wouldn't). uPVC pipe is OK if it's mUPVC (High temp) not ABS. Although looking at the job it probably is incorrect.

Horizontal cylinders should have a circulating return too or destrat pump.
 

Similar plumbing topics

  • Question
The basin & bathtaps will be pretty old to be...
Replies
14
Views
2K
  • Solved
Thanks for the comments fowlerboi. Like you I...
Replies
7
Views
433
  • Question
are you saying they could have come off the...
Replies
18
Views
3K
  • Question
You need a mcalpine V33WM, the site won't let...
Replies
7
Views
666
Back
Top