bengeary

Hi...... Please can anyone help...?

I have a conventional boiler system and my honey well diverter valve stopped working so I was getting heating and hot water at the same time. I drained heating system down and changed the diverter valve for a Drayton brand new one. When using the control panel after fitting you could see it working new valve working moving to water....heating....and in the middle for both. It took along time for the boiler to fire back up as there was air in the system. I bled all the rads.....The bleed valve in the airing cupboard and even opened the drain valve near the boiler to get ait out whereever I could. The boiler finally fired up and the heating and hot water were both working. Then I turned the heating off.... when i turned it back on again the rads won't get warm and the diverter valve is stuck on heating but I'm only getting hot water.... so confused. I drained the rads again. Turned all of upstairs off and filled up downstairs before opening upstairs rads but still no heating. Please can you help. How come the diverter valve was working and now stuck on heating but I'm only getting hot water......really really hot water...?
 
coz you've cocked it up old son, not as easy as you thought is it?

you need to check for correct operation of the 3 port valve for starters using a multi meter if it isnt moving at all. then drain down and use a doc to refill from the bottom up ensuring the motorised valve is set to manual open and take it from there.
 
Ok.....so turned the valve around, got all the air out the system and the rads have heated up. But I have also got hot water. If you put the got water on the boiler doesn't fire up. So I'm getting both now when the heating is on. It's a Drayton diverter valve.....any suggestions? When I had the valve the other way round u could see it moving to heating....or hot water or both.....now when u put hot water on the pump doesn't fire up or the boiler and the diverter doesn't move....I'm confused....
 
Y Plan Wiring.jpg
 
My mate works for bg.....he said it was definitely the diverter....but is on holiday at the minute. ....Im sure all the wiring is fine.....when you put the actuator on do u have to move the valve to a certain position?
 

Similar plumbing topics

C
  • Question
Thanks for replying matey. You've been a...
Replies
3
Views
1K
Heating will run until hot gets up to...
Replies
1
Views
982
Cheers.
Replies
7
Views
781
Are you Gas Safe Registered? If not please...
Replies
2
Views
630
Hi Tony How did you get on with your diverter...
Replies
1
Views
435
Back
Top