Hot water but no heating after oil run out | Boilers | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Hot water but no heating after oil run out in the Boilers area at Plumbers Forums

Messages
1
Hi all, first year in our new home which uses oil. In the summer we used elec only. In the winter we got some oil delivered and used that. The oil has just run out so I switched the immersion heater back on but we now have no heating but we do have hot water? The only thing I can think of is maybe the valve is dead but it seems too much of a coincidence that its packed up at the same time we run out of oil.

Any suggestions on what you think this could be?

thanks in advance!

EDIT: forgot to add that when the oil ran out we had neither hot water or heating (obviously).

UPDATE: I've just tested both of the motorised valves after watching a youtube video. They both appear to be working correctly. ie. resistance when its off. Both behave the same. I am completely baffled!

UPDATE 2: even with hot water and heating on, pipes are cold both sides of both valves. The only hot pipes I can find branch off from the top of the immersion tank.
 
Last edited:
Have you pressed the reset button on the Burner and primed the Oil if it is a One Pipe System? What Boiler is it? The Immerssion is providing the Hot Water at the moment until you get the Oil Fired Heating working.
 
aww running out of oil is the worst thing you can do it can really mess up the normal system. all debris at the bottom of your ur tank might be in the supply and filters uck. its not really a diy fix ....get a good engineer in quick time, tell the truth ..ie not I need a service (seen that many times) and then when its running get him to service it at the same time, new fikters etc and ask him about discount oil suppliers ...he might save you as much as he charges ..bite the bullet ...
Rob Foster aka centralheatking
 
If the oil ran out then boiler will have gone to lockout. Strainer at tank and any inline filters will need to be checked/cleaned, after that the oil pump needs to be bled before the burner will ignite again.
 
Hi all, first year in our new home which uses oil. In the summer we used elec only. In the winter we got some oil delivered and used that. The oil has just run out so I switched the immersion heater back on but we now have no heating but we do have hot water? The only thing I can think of is maybe the valve is dead but it seems too much of a coincidence that its packed up at the same time we run out of oil.

Any suggestions on what you think this could be?

thanks in advance!

EDIT: forgot to add that when the oil ran out we had neither hot water or heating (obviously).

UPDATE: I've just tested both of the motorised valves after watching a youtube video. They both appear to be working correctly. ie. resistance when its off. Both behave the same. I am completely baffled!

UPDATE 2: even with hot water and heating on, pipes are cold both sides of both valves. The only hot pipes I can find branch off from the top of the immersion tank.
so have you bought any more oil yet
 
Fill up oil and get your oil guy to bleed the line. Also get your oil guy to show you how to do it if you feel able.

Also consider getting a watchman or similar to prevent running out in the future.
 

Similar plumbing topics

All fixed. Changing the nozzle and cleaning...
Replies
4
Views
532
Yes everything worked fine before. Is there a...
Replies
6
Views
929
hi, no current pipework in concrete i believe...
Replies
7
Views
1K
It is a Worcester Bosch panel that repaces the...
Replies
2
Views
792
Np Simon. Hoping to get the boiler engineer...
Replies
4
Views
878
Back
Top