Hi,
I wonder if someone could offer me some advice regarding my central heating system?
Everything was working fine up until about a week ago. Suddenly one evening, I noticed that there was hot water, but no heat to the radiators. It was very cold, and it was a week before Xmas, and I have guests coming!!
I am no expert with these things, but did some investigation.
1) The pump is turning
2) The room thermostat is sending a signal to the junction box in the airing cupboard
3) The boiler does fire up - but only until the water is hot. The room thermostat has no effect here.
After reading posts on this forum, and others, I focused on the motorised valve. It looked ancient. I put the switch in manual position, and hey presto - heat!! But only until the water is hot, then it cuts off again.
Ok I thought - and bought a new actuator head. However, sadly after this was installed the behaviour is the same. Hot water - yes. Heating no (well actually I do now get heating int he upstairs radiators while the water is heating up, but to get heating in the downstairs ones I need to put the actuator on manual).
I turned the cyclinder thermostat up, to see if this had an effect. This kicked the heating back into life, and the radiators stayed on for quite a lot longer - long enough to heat the house. But the hot water will now melt the skin off you... so not an ideal situation
So I find myself wondering what the fault could be. Could it be the control box sending only the Hot Water signal? Is the motorised valve not turning enough under the power of the motor, and so not sending the "fire up!" signal to the boiler?
I'd appreciate any advice.
I have an ex council house with an old back boiler. The airing cupboard upstairs has a hot water cylinder, a randall control unit and the pump.
Paul
I wonder if someone could offer me some advice regarding my central heating system?
Everything was working fine up until about a week ago. Suddenly one evening, I noticed that there was hot water, but no heat to the radiators. It was very cold, and it was a week before Xmas, and I have guests coming!!
I am no expert with these things, but did some investigation.
1) The pump is turning
2) The room thermostat is sending a signal to the junction box in the airing cupboard
3) The boiler does fire up - but only until the water is hot. The room thermostat has no effect here.
After reading posts on this forum, and others, I focused on the motorised valve. It looked ancient. I put the switch in manual position, and hey presto - heat!! But only until the water is hot, then it cuts off again.
Ok I thought - and bought a new actuator head. However, sadly after this was installed the behaviour is the same. Hot water - yes. Heating no (well actually I do now get heating int he upstairs radiators while the water is heating up, but to get heating in the downstairs ones I need to put the actuator on manual).
I turned the cyclinder thermostat up, to see if this had an effect. This kicked the heating back into life, and the radiators stayed on for quite a lot longer - long enough to heat the house. But the hot water will now melt the skin off you... so not an ideal situation
So I find myself wondering what the fault could be. Could it be the control box sending only the Hot Water signal? Is the motorised valve not turning enough under the power of the motor, and so not sending the "fire up!" signal to the boiler?
I'd appreciate any advice.
I have an ex council house with an old back boiler. The airing cupboard upstairs has a hot water cylinder, a randall control unit and the pump.
Paul