Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Hot water from boiler expansion pipe in the Boilers area at Plumbers Forums

Status
Not open for further replies.
T

Tech12

Hi: Just joined & have a query, A friend has just had his heating pump replaced. Since the pump was replaced, every time they use the heating / hot water they have hot water / steam coming from the boiler vent pipe in the attic.
He called the plumber that replaced the pump, he says he doesn't have a clue what's going on.
I was thinking either the speed control is set too high or possibly he's installed the pump backwards, but I'm a sparky not a plumber & could do with some advice from those with more knowledge.


Thanks: Andy
 
does sound like the pump speeds to high,try turning it down
 
get a plumber in that knows his stuff, hopefully speed is too high, otherwise blockage, poor system design, oversized pump etc etc
 
Pump is either set too high, or sludge blocking the cold feed and pushing up over the vent. It may of been happening all the time and not been noticed. If the pump was fitted backwards it would probably stop the boiler working.
 
Hi Gasman: Cheers for the reply buddy, appreciate it. Forgot to say: The system is about 20 years old & was working well until the pump popped, you may be onto something though. Apparently the plumber told them he'd fitted a high pressure pump, will ring him tomorrow & tell him to call another plumber.


Andy
 
Last edited by a moderator:
Pump fitted by a clown

Hi Guys: Thanks for the replies, in fairness to the plumber he's done work for me & my customers for over 15 years without any problems. Having said that, that was then & this is now, will see my mate this morning & tell him to get a different plumber in to look at it.


Andy
 
Last edited by a moderator:
Asked a local heating engineer to have a look at it, he's asked me to meet him there tomorrow morning.Will update the thread once he's been.Thanks for the advice so far guys: Andy
 
Hi guys: Apologies for taking so long to update this, plumber didn't turn up (nothing unusual down here). Anyway looked at the pump & it was running flat out on 3, turned it off & back to 2. After a 6 hour run everything seems to be back to normal, thanks for all the replies & help it's much appreciated.


Andy
 
Status
Not open for further replies.

Similar plumbing topics

At the moment when you move the hot water...
Replies
12
Views
1K
200% won’t be the reason the cylinder isn’t...
Replies
10
Views
1K
hi, no current pipework in concrete i believe...
Replies
7
Views
1K
Have you considered a faulty by-pass valve or...
Replies
3
Views
598
There is 6 pipes under the boiler and one goes...
Replies
19
Views
1K
Back
Top