Just joined. hope someone can help. Replaced honeywell room thermostat with same make and model new one. Wired exactly as old one, but now the water only heats when the thermostat is on. Hollybox
 
Thanks for the reply. The boiler is a Baxi Solo.There is also a honeywell programmer fitted to the system. This seems to be working ok. Its a fairly old system but has been working ok until now.Noticed last week that the radiators were staying on when I turned the room thermostat right down, which is why I changed the thermostat.
 
The boiler is a Baxi Solo.There is also a honeywell programmer fitted to the system. This seems to be working ok. Its a fairly old system but has been working ok until now.Noticed last week that the radiators were staying on when I turned the room thermostat right down, which is why I changed the thermostat.
Unfortunately you decided what the solution was before finding the cause of the problem.

As you have a Baxi Solo, you will have a hot water cylinder, which means you will have motorized valves; either one like this:

Honeywell V4073A 3 Port Motorised Valve - NoLinkingToThis, Where the Trade Buys

or two like this:

Honeywell V4043H 2 Port Motorised Valve - NoLinkingToThis, Where the Trade Buys.

The problem is probably in a valve.

How many valves do you have? You will usually find them near your hot water cylinder.
 
Ok sounds about right for me. Only have one valve which is the 3 port as in the picture.I guess I will have to replace this but is it a DIY job I wonder!
That depends on what is wrong with the valve and how old it is. On modern valves the actuator - that's the metal box part - can be separated from the body and replaced on it's own. Faults can develop in either part; it's a case of finding out which. So here goes!

Turn power off. (Turning the timer to HW and CH off is not enough).
This resets the valve to the default position.
Move the lever in the slot to the MAN end.
You should feel resistance as you are opening the valve against a spring.
If there is no resistance, the valve is stuck open.
If there is resistance, release the lever, which should move back to the Auto end.
Do this several times to check if the valve is sticking.

If the valve is sticking, you need to remove the actuator. The method varies depending on make.

If you have a Honeywell valve and the actuator does not have a small bump on the top, the actuator cannot be removed; you will have to get the complete valve changed. That normally means a drain down.

When you have removed the actuator, you will see the valve shaft sticking out of the body. This should rotate easily (about 20 degreed only). If it is stiff, apply a little WD40 or similar light oil to the shaft to see if it frees. If not, you will have to change the complete valve.

If the valve is NOT sticking the actuator needs to be checked.
Make sure the programmer is set to CH and HW OFF and the room and cylinder thermostats are set low.
Turn the power ON
Set HW ON and turn cylinder thermostat up
The boiler should light
Check that the pipe from valve to cylinder gets warm.
Turn CH ON and turn room thermostat up (You should hear the valve move)
Boiler should continue to run
Check that pipes from valve to cylinder and radiators both get hot
Turn HW OFF (You should hear the valve move)
Boiler should go OFF and a few seconds later restart
Check that pipe to cylinder cools down and pipe to radiators warms up.
Turn HW ON
Boiler should go OFF and a few seconds later restart
Check that pipe to rads cools down and pipe to cylinder warms up.
Turn HW thermostat to minimum
Boiler should go OFF and a few seconds later restart
Check that pipe to cylinder cools down and pipe to radiators warms up.


Report findings
 
Really appreciate the time you are taking with me on this problem.I have carried out the tests. No resistance at all when moving the lever from Auto to Man. In fact it is quite loose.I have also carried out the other test.Nothing happens when I turn the HW on and the cylinder termostat up. When I turn the CH on then the boiler lights. When I turn the HW off again the boiler continues to light.The silver box has got a wee bump on top and a small screw on the side.Is this how I remove the actuator? Also just noticed that there is a ticking noise coming from this box when the HW is on and stops when I turn the HW control to off.There is a no on this box if it helps. Honeywell F5 9922.Is an eye opener! never knew so much went on in my heating cupboard.
 

Similar plumbing topics

C
  • Question
Thanks for replying matey. You've been a...
Replies
3
Views
1K
  • Question
OK back early. Too cold! Boiler (hot water)...
Replies
19
Views
2K
  • Question
I wanted to bring this one to conclusion. My...
2
Replies
36
Views
3K
I will have to experiment like you said and...
Replies
6
Views
1K
Sounds more like the heating zone valve isn’t...
Replies
5
Views
1K
Deleted member 120897
D
Back
Top