I have a Glowworm Felxicom CX30. The central heating works just fine, however the hot water does not. The water does get hot but it does not stay hot, it goes cold and then hot again, repeating until displaying error F25.
I had someone to look at it and they told me it would be the heat exchange plate and slo that I need to install a filter.
So, heat exchange was taken off and clean with brick acid although I must say that it did not seem blocked - (I have taken off and repeated this cleaning 3 times in total now) - and I have fit a Magna Clean filter. The whole system has been drained after leaving in cleaning fluid and I have put some system inhibitor in.
Despite all I've done, I still have the same fault - hot then cold 3 time before error F25 come up.
I put the boiler in state Mode and left the hot tap running and below is the sequence it produces. I'm hoping someone can help with a proper diagnosis before we decide that a new boiler is the only option (rather not just before Christmas but we can't keep on with the current situation)
Hot water turned on - time below is when the state number is first displayed:
13 ignition
14 burner on - 9 seconds
16 fan overrun
53 time: temperature difference flow return sensor too high - 30 seconds
16 fan overrun
10 dhw demand - 40 seconds
53 waiting time: temperature difference flow return sensor too high
13 ignition - 1 min 10 secs
14 burner on
98 flow return - sensor check is running demand is blocked - 1 min 28 secs
97 water pressure sensor check is running demand is blocked - 2 min 30 secs
13 ignition - 2 min 38 secs
14 burner on - 2 min 58 secs
53 waiting time: temperature difference flow return sensor too high - 3 min 38 secs
98 flow return - sensor check is running demand is blocked - 6 min 39 secs
F25 - 6 min 48 secs
Any help would be massively appreciated.
Thanks in advance,
Steve
*edit to say that rads have been bled and none of them are holding air
I had someone to look at it and they told me it would be the heat exchange plate and slo that I need to install a filter.
So, heat exchange was taken off and clean with brick acid although I must say that it did not seem blocked - (I have taken off and repeated this cleaning 3 times in total now) - and I have fit a Magna Clean filter. The whole system has been drained after leaving in cleaning fluid and I have put some system inhibitor in.
Despite all I've done, I still have the same fault - hot then cold 3 time before error F25 come up.
I put the boiler in state Mode and left the hot tap running and below is the sequence it produces. I'm hoping someone can help with a proper diagnosis before we decide that a new boiler is the only option (rather not just before Christmas but we can't keep on with the current situation)
Hot water turned on - time below is when the state number is first displayed:
13 ignition
14 burner on - 9 seconds
16 fan overrun
53 time: temperature difference flow return sensor too high - 30 seconds
16 fan overrun
10 dhw demand - 40 seconds
53 waiting time: temperature difference flow return sensor too high
13 ignition - 1 min 10 secs
14 burner on
98 flow return - sensor check is running demand is blocked - 1 min 28 secs
97 water pressure sensor check is running demand is blocked - 2 min 30 secs
13 ignition - 2 min 38 secs
14 burner on - 2 min 58 secs
53 waiting time: temperature difference flow return sensor too high - 3 min 38 secs
98 flow return - sensor check is running demand is blocked - 6 min 39 secs
F25 - 6 min 48 secs
Any help would be massively appreciated.
Thanks in advance,
Steve
*edit to say that rads have been bled and none of them are holding air