long time since i have been on here, wondering if anybody could help me with a problem with a old hot water system on a care home,
the problem i have is no hot water pressure on the second floor, same floor the storage tanks are situated (300 gallons) at least 1 meter head from tap to bottom of tanks
hot water traveling up cold feed and causing tanks to overflow, i have slowed this down by switching off the secondary return but the building now has cold water on ground and first floor, need to run for 5 minutes to receive hot water, ideally need to get the return switch back on asap.
the system has been designed badly, all 40 basins have TMVs as required but not balanced supplies tank fed hot and cold mains water connected to showers and basins i have thought maybe a non return valve is passing and allowing the hot to travel back up the cold feed
i have thought about recommending they change the cylinders to unvented and a accumulator due to low mains pressure (2.5 bar)
any ideas would be a big help, i suppose 2 heads is better than 1
long time since i have been on here, wondering if anybody could help me with a problem with a old hot water system on a care home,
the problem i have is no hot water pressure on the second floor, same floor the storage tanks are situated (300 gallons) at least 1 meter head from tap to bottom of tanks
hot water traveling up cold feed and causing tanks to overflow, i have slowed this down by switching off the secondary return but the building now has cold water on ground and first floor, need to run for 5 minutes to receive hot water, ideally need to get the return switch back on asap.
the system has been designed badly, all 40 basins have TMVs as required but not balanced supplies tank fed hot and cold mains water connected to showers and basins i have thought maybe a non return valve is passing and allowing the hot to travel back up the cold feed
i have thought about recommending they change the cylinders to unvented and a accumulator due to low mains pressure (2.5 bar)
any ideas would be a big help, i suppose 2 heads is better than 1