Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Hot water working, but radiators not. Can anyone solve please? in the UK Plumbers Forums area at Plumbers Forums

Messages
14
Hi all,
I really appreciate any help here - I’m not a plumber and live alone.

Two days ago everything was working fine, but then someone came to do my gas safety inspection and since then my hot water is still normal but my radiators aren’t working.

I have made sure the gas pipe is turned to on (see photo attached) and I have everything set up as it was before (I believe). It’s affecting all radiators and isn’t to do with any being turned off. No errors t comes up on the boiler. I don’t really want to have to call someone back if I can fix it myself…

Has anyone any idea what might have happened / what the gas safety engineer might have done?

Thank you in advance!
 

Attachments

  • 9DDD261A-FA18-47B0-91B1-959EAB4C3947.jpeg
    9DDD261A-FA18-47B0-91B1-959EAB4C3947.jpeg
    330.4 KB · Views: 37
  • D2B198B1-91F0-4272-A8F5-E2915C6C6DE9.jpeg
    D2B198B1-91F0-4272-A8F5-E2915C6C6DE9.jpeg
    244.3 KB · Views: 39
  • 5B2C6AA8-31D5-4C96-9DAA-10846CED4F13.jpeg
    5B2C6AA8-31D5-4C96-9DAA-10846CED4F13.jpeg
    303.6 KB · Views: 35
1. You should have a room thermostat, either mounted to the wall in a room or one you can take around. Make sure this is set to something like 21 degrees.
2. The timer in the centre of the boiler has a black switch in it, at about 10 o'clock on your third photograph. Make sure this switch is on either the timed (picture of a clock) or the on position (usually a 1) and not on the off (O) position.
3. If not either of these I'd suggest you tell the gas safe person they left it not working and ask them to return and fix it as a matter of urgency. In my view there should be no charge unless it is something you have done or a totally coincidental fault.
 

Similar plumbing topics

  • Question
You've fecked up, it's not the way to do it...
Replies
18
Views
2K
  • Question
Thermal store need to keep the cylinder hot...
Replies
2
Views
928
  • Question
Yeah will deffo try I’ve got a strong magnet...
Replies
6
Views
597
  • Question
Will be a 15-60 then prob ups2 Green lights ?
Replies
8
Views
1K
  • Question
Morning, he took it out from where it was...
Replies
11
Views
948
Back
Top