Very bad. Someone has reversed the flow to allow a quasi-S-plan system but that means the cylinder coil flow and return are reversed, the cold feed and vent are reversed, and (could be a serious safety issue) the open vent isn't really open. Needs a competent plumber to modify that into a proper S plan.
Thanks for your replies, what about this set up in the picture? Or would it be a waste of time. The pump and valves are right next to the boiler,
so would be really difficult to get the vent and feed before the pump
That's no safer mate. The vent needs to be off the boiler flow and before the pump ideally you will position the cold fill there as well with the vent first and the cold fill after with a maximum of 150mm between the two centres of the tee's.
Yes for a number of reasons, perhaps most the function and durability of the system is that the vessel should be on the return and with the pump shortly after, this way you will create a positive pressure through the boiler and throughout the system where it meets the vessel connection and point of no pressure change. This will ensure no air is drawn into the system, as well as not allowing any dissolved gases from being drawn from the fluid. Positioning the vessel on the return will also prolong the life of the vessel diaphragm as its not subjected to the higher temperatures.
Whilst the engineer is making the adjustments I would strongly advise a filter installed on the return as well and pay attention to the quality of water when draining down. Your system may benefit from a flush with chemicals.