Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss How does an accumulator work? in the Gaining Plumbing Experience area at Plumbers Forums

Messages
155
Most of the literature on cold water accumulators such as the GAH Coldstream and TWS mains boost show a usable capacity of 50-60%. Is this volume usable in full? Is the initial draw off at the max pressure available (that the accumulator is pre-charged to) and then slowly decreases as the accumulator runs out. Is there a percentage at which the accumulator doesn't add any benefit, despite still holding water?

And one other concept I'm struggling with - at 3.5 bar mains and 2 bar precharge (the recommended setting according to GAH and TWS), the accumulator is supplementing the mains dynamic pressure. Does that mean whichever is the highest of mains or accumulator, that's the dynamic pressure you will be getting? Is it therefore advantageous to have a higher precharge, if your mains is capable of a higher static pressure. Just wondering why 3.5/2 is the "recommended" setting from GAH and TWS?
 
In simple turns it's a big expansion vessel that is set to normally the operating pressure of the system

It doesn't boost pressure it levels out flow rate giving you the same flow as let's say one tap open

You can get some that pump the acculturator upto 6 bar (so doubles your capacity at an op of 3 bar)
 
Most of the literature on cold water accumulators such as the GAH Coldstream and TWS mains boost show a usable capacity of 50-60%. Is this volume usable in full? Is the initial draw off at the max pressure available (that the accumulator is pre-charged to) and then slowly decreases as the accumulator runs out. Is there a percentage at which the accumulator doesn't add any benefit, despite still holding water?

And one other concept I'm struggling with - at 3.5 bar mains and 2 bar precharge (the recommended setting according to GAH and TWS), the accumulator is supplementing the mains dynamic pressure. Does that mean whichever is the highest of mains or accumulator, that's the dynamic pressure you will be getting? Is it therefore advantageous to have a higher precharge, if your mains is capable of a higher static pressure. Just wondering why 3.5/2 is the "recommended" setting from GAH and TWS?
When precharged the accumulator is full of air at 2 barg = 3 bara, and fills total accumulator volume. When connected to the water at 3.5 barg = 4.5 bara, the air is compressed and reduces in volume to 3/4.5 = 0.67 x total volume. So water inflow = 0.33 x total volume.
It's possible, but unlikely, that the 2 and 3.5 bar are absolute, in which case the water inflow = 1 - 2/3.5 = 0.47 x. Not sure where they get 50-60% from, maybe whoever worked it out calculated wrong!
 
At 33% capacity, the benefit of even a 500l accumulator seems pretty pathetic.
It depends what you're trying to do with it. If it's on a hydropneumatic system with maximum say 20 pump starts/hour, it's OK for pump flow 13 m3/h, which doesn't seem too bad. Though in practice a smaller vessel would normally be used, with a minimum run timer set at 3 minutes to limit start frequency.
 
It depends what you're trying to do with it. If it's on a hydropneumatic system with maximum say 20 pump starts/hour, it's OK for pump flow 13 m3/h, which doesn't seem too bad. Though in practice a smaller vessel would normally be used, with a minimum run timer set at 3 minutes to limit start frequency.

most accumulators arnt pumped
 
An expansion vessel in a boiler isn't an accumulator
 
Boosting/ equalising his flow from the mains when multi taps / outlets are in use
 
It's the safe figure you shouldn't get anywhere near that but you could if you have a few problems/ things not accounted for
 
Always go for worse case and I always over spec / oversize them
 
Boosting/ equalising his flow from the mains when multi taps / outlets are in use
Good point, I should have read the original post more carefully.
Looking at the GAH website, Model 500 has gross capacity 450 litre, maximum water content 292 litre. Minimum precharge pressure 0.5/0.8 bar (whatever that means!).
With 3.5 barg mains and 0.5 barg precharge, air volume after pressurisation = 450*1.5/4.5 = 150 litre, and water inflow = 450 - 150 = 300 litre. It says you would only use lower precharge pressure (below the standard 2 bar) if the mains pressure is low, so water content 292 litre (>60%) seems to be very much a maximum figure.
 