Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss How does water work in flat, is this right? in the UK Plumbers Forums area at Plumbers Forums

Messages
276
Hi everyone, just a question for my own knowledge and understanding of how water works in my flat and making sure everything complies with water regulation in the UK. , The flat is circa 1960s used to have a hot water cylinder and cold water tank in the cupboard but since late 90s or early 2000 was replaced with a combi boiler for DHW and CH in the flat.

Does the following seem right and current with UK water regulations and do I need to change anything?
  • Top floor flat, hot and cold is via mains water feed, Combi boiler (8 months old) 1.5 pressure bar on combi boiler.
  • Have mixer taps in bathroom (bathtub and basin) and single lever mixer tap in kitchen, thermostatic mixer shower, all hot and cold pipes in bathroom and kitchen have isolation valves fitted on them.
  • The Main Cold Water Feed Pipe in the utility cupboard has a 22mm Non Return Valve fitted on it.
  • Hot water pipe under kitchen sink has a check valve on it
Do I need to add any NRV's/check valves to any of the pipes in the kitchen or bathroom or does it all seem legit. As mentioned I live on the top floor and have another 2 flats below me.

Any information or advice would really be appreciated as I am interested in knowing how things work thank you.
 
Hi Bobbyjoe,

You have what’s generally referred to as balanced supplies so the hot and cold are of similar if not equal pressure. Providing your taps have an adequate air gap between the spout end and spillover level, then all should be good. Your shower shouldn’t be able to fall into the bathtub or within (usually) 25mm if spillover level, the spillover level of the wash basin, bidet or wc pan.

See this for a bit more clarity: https://www.wras.co.uk/downloads/pu...flow_in_the_design_of_domestic_bathrooms.pdf/
 

Similar plumbing topics

  • Question
Thanks for the reply and information so far...
Replies
7
Views
1K
  • Question
The water should come out no hotter than the...
Replies
3
Views
857
  • Question
Thank you and from what my neighbours have...
Replies
2
Views
823
  • Question
Mostly all should but there’s no requirement...
Replies
6
Views
712
Back
Top