I have a single lever pull out kitchen faucet installed. The tap takes a hot and cold water connection, the cold is from the mains so is at a higher pressure. The hot is from the system boiler so is at a lower pressure. It seems to me that when I open the tap, the cold water is forcing its way into the hot water pipe due to the pressure difference. Is there anything that can be done to prevent the reverse flow?
 
The pressure reducing or equalising valve on the cold, though, you could do now, with the existing tap. It would limit your pressure, but you'd have better mixing from your tap. Depends, though, whether successful mixing is more or less important than a good jet from your cold and only you can know how you tend to use your tap.
 
Thanks Ben
The pressure reducing or equalising valve on the cold, though, you could do now, with the existing tap. It would limit your pressure, but you'd have better mixing from your tap. Depends, though, whether successful mixing is more or less important than a good jet from your cold and only you can know how you tend to use your tap.
Thanks for input Ric, so mixing is definitely important but at the same time, I do plan to replace the current system boiler with a mega flow system in the near future which hopefully should take care of the pressure issue. So which one would be a better option, a pressure reducing valve on the cold or a single check non return valve on the hot or should I go for both?
 
Thanks for input Ric, so mixing is definitely important but at the same time, I do plan to replace the current system boiler with a mega flow system in the near future which hopefully should take care of the pressure issue. So which one would be a better option, a pressure reducing valve on the cold or a single check non return valve on the hot or should I go for both?

If you fit a PRV, you don't need a check valve.

As Ben-Gee has suggested a check valve less than £5 in UK, while a PRV can cost around £30. So depends how temporary this has to be.

If you go for the check valve, you need the check valve on the higher pressure side, so I would put it on the cold in your case - not the hot!
 
If you fit a PRV, you don't need a check valve.

As Ben-Gee has suggested a check valve less than £5 in UK, while a PRV can cost around £30. So depends how temporary this has to be.

If you go for the check valve, you need the check valve on the higher pressure side, so I would put it on the cold in your case - not the hot!
The current plan is to have this sustain for the next 3-5 months until I sort out the build plans. I am a bit confused, why would the NRV be on the cold pipe, shouldn't it be on the hot water pipe to prevent the cold water from flowing back in?
 
Apologies for paragraph 3 in post #9 which is completely incorrect. As Ben-Gee has correctly noted, the NRV should be on the hot not the cold!

Do bear in mind the classic spring-loaded NRV will have a detrimental effect on the flow/pressure of the hot water.
 
I have a single lever pull out kitchen faucet installed. The tap takes a hot and cold water connection, the cold is from the mains so is at a higher pressure. The hot is from the system boiler so is at a lower pressure. It seems to me that when I open the tap, the cold water is forcing its way into the hot water pipe due to the pressure difference. Is there anything that can be done to prevent the reverse flow?
Put a pressure reducing valve on cold main before it goes to tap
 
Apologies for paragraph 3 in post #9 which is completely incorrect. As Ben-Gee has correctly noted, the NRV should be on the hot not the cold!

Do bear in mind the classic spring-loaded NRV will have a detrimental effect on the flow/pressure of the hot water.
No worries Ric, Thanks to you and Ben for guiding me. Are there any alternatives to the classic spring-loaded NRV's?
 
Yes. You can get swing valves. Technically they don't meet the legal criteria for backflow protection but in this case you are making an existing system more compliant than it previously was, so I wouldn't over-worry about that.

Having said that, swing valves are not as cheap as the spring-loaded ones and the difference between a NRV and a PRV is now less.
 
That’s liveable with if it proves to be the case, however I have done this often and find a warm blend is available, obviously only add in a bit of cold.
The idea is to stop the cold back filling the cylinder and ultimately the CWS , I’ve seen the aftermath of this and it’s not pretty.
The OP is also updating system soon.
 

Similar plumbing topics

  • Question
Hi, I'd be grateful for some advice please...
Replies
0
Views
222
  • Question
Morning, he took it out from where it was...
Replies
11
Views
957
  • Question
Marcin whilst your understanding of a pressure...
Replies
2
Views
857
  • Question
I believe a dual flow tap does not require non...
Replies
3
Views
939
Back
Top