I want to replace a Danfoss T6360B with Digital One? | Central Heating Forum | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss I want to replace a Danfoss T6360B with Digital One? in the Central Heating Forum area at Plumbers Forums

The T6360B will have 3 terminals, 1,2&3. the brown wire which is from the programmer CH, is connected to 1, 3 is the switched live which may be green/yellow which starts the boiler. 2 is neutral which may have a blue wire attached to it, this (accelerator) is used to heat a little resistance when the stat is closed and makes the stat switch off at a lower hysteresis, it is not used in my digital Fantini Cosmi digital Stat.
 
The T6360B will have 3 terminals, 1,2&3. the brown wire which is from the programmer CH, is connected to 1, 3 is the switched live which may be green/yellow which starts the boiler. 2 is neutral which may have a blue wire attached to it, this (accelerator) is used to heat a little resistance when the stat is closed and makes the stat switch off at a lower hysteresis, it is not used in my digital Fantini Cosmi digital Stat.
I certainly hope if there's a bare copper wire with a green/yellow sleeve on it, that it's not being used for switched live!
That wouldn't comply with wiring regulations In Stockport!
 

Similar plumbing topics

A
Not sure why you’d replace the pcb without due...
Replies
1
Views
863
Deleted member 120897
D
There seem to be many smart thermostats now...
Replies
6
Views
838
Thanks shauncorbs
Replies
4
Views
1K
Many thanks. followed your advice and works...
Replies
2
Views
2K
Replies
14
Views
1K
Back
Top