Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss I wish to add a second boiler to my existing meter. Location 20m away. in the Boilers area at Plumbers Forums

Messages
5
I wish to add a second boiler to my existing meter. Location 20m away. Underground run. Can l use 32mm yellow pipe with copper tails at each end. Thank you in advance
 
What size are your existing and proposed boilers kw
 
Hi Shaun. Thank you for the reply. Both 9kw. Will the meter be able to supply that volume of gas....

So heat only boiler in theory yes you should be fine providing the gas safe engineer works out there pipesizing etc
 
It's a 6m3/h meter Shaun will that cope with 18kw.... Is there any reason l can't use 35mm plastic yellow gas pipe after the meter under the ground. Thank you. Matt

Yes stnd domestic meter

The gas engineer can but it’s a bit more labour in installing it as it needs special fittings and practices to terminate above ground
 

Similar plumbing topics

I get 1.65mB drop plus fittings for 30m in...
Replies
18
Views
3K
Replies
15
Views
2K
Anyway, you can always increase the boiler...
Replies
16
Views
1K
The boiler is just responding by limiting the...
Replies
8
Views
1K
Fair point. There is a dearth of heating...
Replies
9
Views
1K
Back
Top