Hiya. First post.. please be gentle :wink5:
I've got an ICOS HE24 Boiler fitted to a Megaflo Cylinder. All about 6 years old. All - until recently - was in perfect working order. The problem I have is strange, so I'll jump straight in - please bear with me and read on.
I've:-
Finally, there is another problem
Its the height of summer. All my room 'stats are "OFF" with the little switch on the side.However the rads are getting warm - downstairs only. This might be that dodgy valve ?
How does the room stat work ? I thought it sent a signal to the controller to spin the pump which then was seen as a low temperate water demand to the boiler which then said "boiler, please light"... I might have got this wrong.
Given that
a) The pump clearly works
b) The valves clearly work
c) The controller is clearly OK....
You can see I'm puzzled. Why does (all of a sudden) the upstairs demand for heating not result in a boiler light up ?
ALL THOUGHTS and OBVIOUS STUFF please welcome !..
Thanks
S
I've got an ICOS HE24 Boiler fitted to a Megaflo Cylinder. All about 6 years old. All - until recently - was in perfect working order. The problem I have is strange, so I'll jump straight in - please bear with me and read on.
- Zoned system - up and downstairs.
- I've replaced the boiler control board 3 years ago with the new V9 (it was failing to light) - all ok when it was installed.
- All rad valves are thermostatic - 2 years old - perfect working order.
- Until recently- All was well.
- Hot water is still fine.
- Downstairs is still fine - i.e. flick the 'stat over (orange light on the room 'stat is lit) and voila, the boiler lights - rads heat up
- Upstairs - doesn't work - but hang on, it does.... bear with me.
- If the downstairs is "on / working".. and the upstairs stat is then set to "on" then the upstairs rads warm up as usual until the temperature is reached upstairs.
- However, if the downstairs zone is "off" , but the upstairs is "on" (orange light on) then the boiler doesn't light.
- In other words... the only time upstairs rads get hot.. is when the downstairs circuit is working
I've:-
- Mechanically checked all the zone valves in the airing cupboard. (the little qtr turn jobbies). Mechanically, they move well, no leaks
- I've checked that downstairs room stat moves the zone valve OK
- I've checked that the upstairs room stat moves the zone valve - A little sticky to return to normal... so in fact this is suspect, but manually operating has no effect on the fault.
- There is another valve which operates the water to the hot water cylinder. This is wierd... even though hot water is fine, there appears to be a demand from "something" for hot water. In other words, with all circuits switched to OFF and HW on the timer to OFF, the boiler can light. ! Not sure what's going on here
- I've tried my next door neighbours controller.. their sytem is by chance identical - no change.. I still have troubles.
Finally, there is another problem
Its the height of summer. All my room 'stats are "OFF" with the little switch on the side.However the rads are getting warm - downstairs only. This might be that dodgy valve ?
How does the room stat work ? I thought it sent a signal to the controller to spin the pump which then was seen as a low temperate water demand to the boiler which then said "boiler, please light"... I might have got this wrong.
Given that
a) The pump clearly works
b) The valves clearly work
c) The controller is clearly OK....
You can see I'm puzzled. Why does (all of a sudden) the upstairs demand for heating not result in a boiler light up ?
ALL THOUGHTS and OBVIOUS STUFF please welcome !..
Thanks
S