Icos HE24 / Megaflo - boiler comes on when it should not | Boilers | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Icos HE24 / Megaflo - boiler comes on when it should not in the Boilers area at Plumbers Forums

Status
Not open for further replies.
C

clubsport911

This forum helped me recently with a fault and now I've found another. In fact, the system has been a little wierd lately... Read on.

This morning at 3 am I was woken up by missus who had been up for half an hour worrying why the boiler was on and not going off.

It seems that indeed, the boiler was on and from the heat in the utility room had been on for a while.

None of the room stats were calling for heat
No hot taps were on
The timer controls were all inactive (no red lights)

Yet, the boiler was on.

The downstairs rads were in fact a little warm but not hot.

I then went to the timer (Horstmann) and pushed the programmer to OFF on all CH and HW. Went downstairs and switched the boiler off with the mains switch.

I then switched it back on, the fan came on, and once again, it fired up.

Where on earth is the boiler getting its ON signal from ? For the last fault, I managed to prove my boiler controller was ok by substituting with my neighbours, but this has stumped me.

Surely, the timer has control over the boiler ?
How can the boiler be fired up if the timer is off ?
Where do I start looking ?

Thanks for all your help !

PS in all other ways, the system seems fine....
 
It was one of the Honeywell valves. it was sticky so the return spring wasn't enough to remove the pressure from the microswitch.

Stripped out the valve, lubed (fitted an extra spring for good measure)

Presto... it works fine !

Thanks to BEWSH and lame plumber for your replies !
 
Status
Not open for further replies.

Similar plumbing topics

That solved it ! But why do plumbers fit...
Replies
12
Views
1K
Yeah I think Ill have a Hive thermostat in...
Replies
4
Views
589
S
Boiler Fault I’m hoping someone can help with...
Replies
0
Views
130
S
Yes, it looked like water had leaked on it...
Replies
4
Views
2K
Someone has said, he wouldnt of plumbed it as...
2
Replies
36
Views
3K
Back
Top