Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Ideal Boiler No Hot Water in the Boilers area at Plumbers Forums

Status
Not open for further replies.
D

davecpfc

Hi

Hope this is in the right place, looking for some advise.

I have an Ideal Icos HE24 boiler and today it has stopped heating water. It has power running to it, both the time display and boiler.
The source code is 0 but the light for the burner doesn't come on and holding reset doesn't do anything.
I have turned the whole boiler off and turned back on, when I do this it flashes 4 once and then goes to 0 on the source and has no bar of pressure showing.

Is there anything I am able to do?

If you need any further details please let me know and thanks
 
Call in an engineer there is a 99% chance there is nothing you can do. And the 1% you have already tried.
Maybe post in the i need an engineer section
 
Do you know how to top up pressure in system, if its showing Zero that's why its not working.
 
Topping an icos up ??
Id be surprised if its a sealed system..but possible
 
Last edited by a moderator:
Do you know how to top up pressure in system, if its showing Zero that's why its not working.

Thanks for the replies, wouldn't have a clue how to do this? am I best as Phill suggests to get an engineer in?
 
Have you a water tank or 2 in the loft or a high upstairs cupboard ??
 
Can you see any sort of expansion vessel. It will be made of steel and spherical should be/usually red
 
So must be a filling point with a pressure gauge somewhere near the red tank may look like a chrome hose with black leaver or if cheep one screwdriver slot, can you put on photo of airing cupboard ??
 
Also can you see sort of water coming from a pipe outside near the location where the boiler is, but on the outside.
It may be dripping or the brickwork wet and hard to see.

If you add photos its worth a 1000 words
 
image-18-10-15-02-27-1.jpgimage-18-10-15-02-27.jpg
So must be a filling point with a pressure gauge somewhere near the red tank may look like a chrome hose with black leaver or if cheep one screwdriver slot, can you put on photo of airing cupboard ??
 
On me phone atm so pics are small back right 1st set of pipes looks like a filing loop will look like a washing machine valve with a flex on the end going to another washing machine valve
 
Can you take a photo on the right hand side of the hot water tank cant make out what is in that corner, I can see a gauge on the pipe work , what is that reading ? the chrome flexi that you are showing is the expansion from the tank , is the one on the right hand side the same sort of pipe ??
 
I might be missing something but 0 on an Icos is no demand at boiler. C sw live received foe boiler. Could be controls
 
Can you take a photo on the right hand side of the hot water tank cant make out what is in that corner, I can see a gauge on the pipe work , what is that reading ? the chrome flexi that you are showing is the expansion from the tank , is the one on the right hand side the same sort of pipe ??
image.jpg
image.jpg
Hope they help..
Turns out the heating filling loop was closed, opened that and the tank has now filled but still doesn't seem to be kicking out heat or hot water. Once I open the heating loop the pressure bar went from 0 to just over 3
 
View attachment 23453
View attachment 23454
Hope they help..
Turns out the heating filling loop was closed, opened that and the tank has now filled but still doesn't seem to be kicking out heat or hot water. Once I open the heating loop the pressure bar went from 0 to just over 3

turn the filling loop off and its too full needs to be around 1-1.2 bar to get the pressure down bleed a rad
 
I might be missing something but 0 on an Icos is no demand at boiler. C sw live received foe boiler. Could be controls

Yes that is correct 0 is no demand but even without tap running nothing changes and heating not kicked in even though on at control
 
Take it all controls are calling for heat ? Room stat turned up, on at timer etc.,
 
Status
Not open for further replies.

Similar plumbing topics

Which Vaillant boiler is it?
Replies
1
Views
360
W
pcb issue so gas safe engy required sorry to say