It says in the manufactures instructions that a 24kw ideal boiler will work ok with a gas inlet pressure of 14mb or more. With a working pressure at the meter of 19-23mb this will be far greater than the allowed 1mb drop for the pipework. They allow 1.5mb drop for the gas valve too. If installed with a 14mb inlet pressure it isn't to gas safe regs. I ask as I have looked at a job where there is around 5-6meters including bends of 15mm copper from the meter that goes in a sold floor chase and up to the old non-condensing boiler. A 24kw boiler needs 2.28m3/h of gas the current pipework will supply around 1.9m3/h. To take the supply up to 22mm would be a huge job with a lot of disruption. Would the 15mm pipe likely be ok in this situation? Another note there is no other gas appliances in the building.