Hi
I have an Ideal Classic SE18FF that is showing its age and cut out and won't restart today. I've checked it gets a signal from the room thermostat and timer and the central heating pump is running but there is no spark through the viewing window or across the PCB component referred to as the SG1 tube in the manual so it doesn't fire up. (no idea what that component is but daren't touch it with the multimeter)
The PCB has power (the single LED is lit and the two relays switch when there is a signal). I can hear the fan but when I place my hand against the flue outside I can't feel any airflow (don't know if that is normal). The red and violet wires on the air pressure switch are live but the yellow wire isn't. If I unplug the fan from the PCB the voltages on these pressure switch wires don't change. The fan has about 70 ohms resistance across it so I don't think it has burnt out.
Would really appreciate a steer on what's gone wrong before I get the professionals in. Have worked through the fault finder diagnosis chart in the manual but it is inconclusive. I reckon either:
1. the PCB - which looks easy enough to swap but an expensive gamble if I'm wrong
2. the fan - which can't have burnt out but has maybe slowed right down so it is not creating enough of a pressure gradient across the pressure switch
3. the pressure switch - as it gives the same signal regardless of whether the fan is on or disconnected
If it is 2 or 3 then over to the professionals. Would be very helpful to know the likely cost and complexity so I know what I'm letting myself in for.... or if there is a cheap fix an amateur can do safely.
Many thanks
Stuart
I have an Ideal Classic SE18FF that is showing its age and cut out and won't restart today. I've checked it gets a signal from the room thermostat and timer and the central heating pump is running but there is no spark through the viewing window or across the PCB component referred to as the SG1 tube in the manual so it doesn't fire up. (no idea what that component is but daren't touch it with the multimeter)
The PCB has power (the single LED is lit and the two relays switch when there is a signal). I can hear the fan but when I place my hand against the flue outside I can't feel any airflow (don't know if that is normal). The red and violet wires on the air pressure switch are live but the yellow wire isn't. If I unplug the fan from the PCB the voltages on these pressure switch wires don't change. The fan has about 70 ohms resistance across it so I don't think it has burnt out.
Would really appreciate a steer on what's gone wrong before I get the professionals in. Have worked through the fault finder diagnosis chart in the manual but it is inconclusive. I reckon either:
1. the PCB - which looks easy enough to swap but an expensive gamble if I'm wrong
2. the fan - which can't have burnt out but has maybe slowed right down so it is not creating enough of a pressure gradient across the pressure switch
3. the pressure switch - as it gives the same signal regardless of whether the fan is on or disconnected
If it is 2 or 3 then over to the professionals. Would be very helpful to know the likely cost and complexity so I know what I'm letting myself in for.... or if there is a cheap fix an amateur can do safely.
Many thanks
Stuart