Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Ideal he 24 c heating but no hot water in the Bathroom Advice area at Plumbers Forums

gingalig

Gas Engineer
Messages
217
Hope I can get some advice, called out to a no hot water issue , I have checked theoperation of the actuator and the diverter all seems ok, I’mabout to order a DHW flowswitch , the boiler fires forheating and the heating works fine, and a very small amountof hot water will arrive at tapsbut then flows cold, heating off and there is again a tiny amount of warm water then flows cold, apologies if I’m asking obvious questions, I’m a bit new to diagnostics. Thank you in advance for any advice.
 
Hope I can get some advice, called out to a no hot water issue , I have checked theoperation of the actuator and the diverter all seems ok, I’mabout to order a DHW flowswitch , the boiler fires forheating and the heating works fine, and a very small amountof hot water will arrive at tapsbut then flows cold, heating off and there is again a tiny amount of warm water then flows cold, apologies if I’m asking obvious questions, I’m a bit new to diagnostics. Thank you in advance for any advice.

Presuming that we're both thinking of the same Boiler.
Have a look through the manual here and follow the fault chart. It tells you how to test the DHW side. There are a few things to check. See page 49.
 
As above bud. Good luck kop

Screenshot_2018-02-02-10-57-55.png


Screenshot_2018-02-02-10-57-20.png
 
Down load the manual find the page you want screen shot it then upload it from there Last i think your putting yourself down a bit bud its pretty cool how you put the whole manual in the word ( here) . cheers kop
 
I've done a lot of repairs due to the turbine failing very easy to change but I would change the flow sensor as well

Very easy to do and less than 10 mins to change both
 
I've done a lot of repairs due to the turbine failing very easy to change but I would change the flow sensor as well

Very easy to do and less than 10 mins to change both

Excuse my ignorance/lack of knowlege is that the magnetic flow switch (the turbine ) I have changed the flow sensor and initially it worked , called for heating and it still worked then hot water stopped. turned off the power and then calling for hot water all worked well again, checked multiple times then it stopped firing for hot water again. turn the power on and then off and it all works fine for a while. ?? then stops again, Looking through the M.I's and it seems to be pointing to a PCB fault although this was apparently changed less than a year ago. Any thoughts It's giving me a headache.
 
Yes

The switch should light up constant red led if it doesn't change the mag flow switch
 

Similar plumbing topics

Are you Gas Safe Registered? If not please...
Replies
2
Views
536
Looks that way, a multimeter would tell alot...
Replies
8
Views
862
  • Question
Problem found, it was a blockage... mostly in...
Replies
11
Views
1K
P
  • Question
Could be the diverter (more likely than...
Replies
1
Views
878
Deleted member 120897
D
  • Question
I don't see your comments?
Replies
8
Views
711
Back
Top