Hi there guys.
Im looking at a Ideal Icos HE 12 ( i know destroy the piece of S...) on a unvented cylinder S plan system.
First of all the heating wasnt working which turned out to be a faulty motorised valve on the heating side.
When i call for hot water it fires up then locks out on H:A error code with some banging noises. Which i gather means its overheating. Condensate trap is clear and there seems to be no air in the system, and pump is fine.
If i run the heating (everythings fine) then call for hot water at the same time, it works, and favours the hot water, all is fine. Turn off CH demand boiler locks out with H:A error.
Anybody have any ideas?
I would say swap the boiler but its for a friend and would help them out if i got it going.
Thanks in advance for any help.