Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Ideal Imini no hot water???? in the Bathroom Advice area at Plumbers Forums

fubar1000

Gas Engineer
Messages
199
Morning chaps

Had a call out to the above boiler yesterday with no hot water. C/H working fine

Popped the front cover off, run the hot tap, internal pipe work from burner to H/W heat ex was hot but the H/W heat ex was cold.

Burner fires up as should, fan runs as should & showing NO fault codes.

Was thinking blocked H/W heat ex but the flow at all outlets is fine. Could it still be a blocked heat ex?

Thanks peeps
 
Had the same last week was told no hw got there not going to fault firing seemly working correct but no hw. It was a sticky diverter bypassing around htg, prob a part blocked hw hex as well. Shut iso on boiler to confirm, removed diverter pull apart clean up with wire wool on pin regrease now all good.
 

Similar plumbing topics

  • Question
Thanks KoP. I plan to replace my boiler later...
Replies
2
Views
2K
They were quite accurate IMO and might look...
Replies
12
Views
1K
  • Question
You need a mcalpine V33WM, the site won't let...
Replies
7
Views
666
Thanks for the confirmation. Having watched...
Replies
4
Views
1K
New flow sensor and we now have hot water.
Replies
5
Views
772
Back
Top