My Dads been having trouble with his Isar M30100 for a few months now. First time I've worked on one of these, as I know there reputation! If its an easy fix I will sort it, if not its new boiler time. As i dont have a great deal of experience with these, I'm looking for some advice.
CH works fine, when the DHW is running, it runs for approx 30 secs then cuts back to low burner, stays at that for a bit then back to high, and carries on like this. I suspected the DHW thermistor, but at £35 from Partscenter its not a cheap trial and error. Resistance was hard to take, with the water running, but at its hottest setting it was around 8-9kohms.
Also the heat it passing down the flow a bit, and the inlet pressure is only 12mbar (Gas pipe is 15mm from the meter, about 12-14m of pipework) But I didn't think these issues would cause the burner to go to low.
Any help appreciated folks
CH works fine, when the DHW is running, it runs for approx 30 secs then cuts back to low burner, stays at that for a bit then back to high, and carries on like this. I suspected the DHW thermistor, but at £35 from Partscenter its not a cheap trial and error. Resistance was hard to take, with the water running, but at its hottest setting it was around 8-9kohms.