Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss ideal isar L9 problem. surprise, surprise! :( in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
B

baldy874

hi. i wonder if anyone can shed any light.

i have an ideal isar he30. error code, L9. on reset it went onto 3 horizontal bars which according to the book, they do this until the heat exchanger drops below 50.

i've read a load of posts here, and so far i have drained the boiler down, removed the condense trap and cleaned. all fine. removed plate exchanger and washed through, but that was all clear too.

not sure if my multimeter is pants because i can get any readings from the dry fire thermistor or the control thermistor.

fired it back up and it went straight onto L9 again and fan went beserk and all got rather hot, rather quickly,

any ideas please? got the wife whining she's cold already!
 
Put some water in the system!!!

Re-pressurise to at least 1 bar.... You GSR?
 
pressurised to just over 1 bar.

not GSR. fairly competent and know my limits.
 
Then next sage is check the pump is working and the boiler is filled with water ... AAV open etc!

:)
 
pump appears to be running ok. AAV not touched. all went cold when i filled it back up and pressure went down to half a bar when i opened isolators, so assume all full with water.
 
re-pressurised to 1 bar for sure ... if the aav is open then 't' will run untill hot water pre-heat is satisfied then the boiler will change to 'c' and circulate through heating ... what stage does the boiler shut off to L-9?
 
just drained down and refilled again.

fired it up, went onto "d", burner light came on, heated up very quickly then went onto L9 in about 20 seconds.
 
oh. on fire up display went "0" - "5" first before "d" and burner light.
 
Definitely sounds like the heat exchanger is dry ... 'd' is hot water demand .. same a 't' as far as the diverter is related ... I'd be checking the aav to make sure its open .. a nightmare of a position to be honest!!!

If you're sure the pump is running then then it sounds like water is not! Could be pump impeller has dislodged? Unusual!!!!
 
wierd.

got some air out of the AAV but still goes to "d" and fires the burner on start up? hot taps all bled btw.
 
and yes, the designers of this trash should be locked up! i've read about a LOT of problems with them.
 
Alas until you get the water to heat up the integral plate hex you are at a loss ... Unless you can remove the actuator and mess with the diverter?
 
aye. will whip that out next. just had pump out and quicklt flicked power on for a couple of seconds. pump 100% working.

cant understand why as soon as i turn it on, it's calling for hot water and firing up?
 
aye. will whip that out next. just had pump out and quicklt flicked power on for a couple of seconds. pump 100% working.

cant understand why as soon as i turn it on, it's calling for hot water and firing up?

They have a built in preheat. If Hws thermister says cold it will heat that first
 
No of that's toast it just won't work
 
would a toasted thermistor cause it to demand hot water first on fire up pre heat?

if i recall, it normally goes to "t" then stright to "0" and ready for action.
 
It's 12:20. Call a GSR in the morning.
 
Hope I am not to late for this one.

I have had 2 of these faults this week.
Look at the front of the pump and if it is an MP61 pump they intermittently stick or run slow giving this fault.

I have had a hell of a job tracking it down as the pump does run and Diverter and motor changed.

Try using a screwdriver as a stethoscope on the pump head and you normally hear a ticking noise (impellers catching).

If not the fault in this case I hope it helps someone?
 
your right there the designers who thought of this boiler want stringing up by there balls ive had nowt but trouble with my boiler this year
 
it was the pump sticking in the end. i took the pump out and fire it up and it span nicely, which is why i ruled it out as a problem!

got it all sorted when my trusty gas man came round the morning after. :)

they are indeed a totally sheite boiler and we are now putting a bit of dosh aside to replace with a nice worcester bosch in the spring!

BIG thanks to all the advice and help here. true gents! :)
 
God these boilers are cak
ive got this problem on an isar he30 3 horizontals im looking at this afternoon before anyone asks yes im gsr and can work on boilers problem is im new to diagnostics yes i have done a course but still greener than th hills. if im successful and it works i will be chuffed gonna disconect the dryfire thermistor for 5 mins if that fails try turning the pump manually if that fails i will ask advice from the wiser heads.
 
Status
Not open for further replies.

Similar plumbing topics

Yes Shaun I could see it dripping from the...
Replies
16
Views
451
  • Question
Thanks Stu. Will get someone out ASAP Been...
Replies
2
Views
3K
Other than pcb not really other than standard...
Replies
3
Views
1K
M
  • Locked
Do full service, check insulation panels and...
Replies
7
Views
166
M
  • Locked
Hi Matt welcome to the forum please get your...
Replies
5
Views
2K
Rickster123
R
Back
Top