Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Ideal ISAR M30100 flame going out in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

Kewat66

Gas Engineer
Messages
119
Hi All,
i am looking at a fault on an ISAR M30100. Boiler fires up ok but after a few hours it goes out and comes up with an LF code. I am thinking of changing the flame sensor as it seems similar to the manual suggestion but this states the boiler goes out after 10 seconds. Is there anything else to look out for on this model?

Thanks
Kewat66
 
Have you checked the temp differential.
Has it trvs all over?
Have you opened wide all trvs (if fitted)
Flow and return differential should be no more than 20 degrees.
If it is can give LF lockout.
 
Condense trap partially blocked?

Remember to check the insulation/ pins on it as well.
 
Ye, check the condense pipe and trap for blockages. Also, really important on the m series, check the insulation pads and pins as a matter of urgency. Unless the orange sticker is on the front, then you can relax a little.
 
Ye, check the condense pipe and trap for blockages. Also, really important on the m series, check the insulation pads and pins as a matter of urgency. Unless the orange sticker is on the front, then you can relax a little.

I always ignore the orange sticker. I would rather physically check
 
Always check the actual wire on an icos/isar. They become brittle and crack shorting to the case
 
Sorry guys bit confused. What do you mean by insulation pass & pins?

They had a major problem on these boilers (all isars and icos) where the burner insulation falls down and blocks the top of the heat exchanger then the boilers kill themselves.

They did new pins for the boiler which looked like a coat hanger but they warp out of shape massively so now they have changed them again. Just pop the fan and burner off and inspect.

Should look like this

e901662da2d8716105c0a67a744c1bc1.jpg


And not like

ed2d7311e028d21a9d567710c6225255.jpg
 
Status
Not open for further replies.

Similar plumbing topics

I also noticed that the pressure gauge is...
Replies
5
Views
1K
Sandeep
S
Probably a pressure sensor still involved but...
Replies
3
Views
1K
Unfortunately most household insurance...
Replies
16
Views
2K
..Thanks, i am wondering if we can keep the...
Replies
7
Views
1K
Back
Top