i have an issue with Logic 30. Keeps coming up with L2 fault code. Have checked gas pressure, cleaned out condensate and still no joy. It runs through the sequence but will not fire. Anyone know of any simple or common faults on these?
Ignition failure. Check previous post on this page under Ideal Independent, same boiler and fault. Likely to be the above but I had a strange one as described in the post
If condo is blocked down the line it can cause lockout, you could take the long flue outlet off and pour water down the condo route to see if it backs up
Also had one last week with the same issue. Was told the air ways in the heat exchanger are blocked. Remove the fan and burner then wash it down with hot water.