Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Ideal logic 35 banging in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

shyguy2005

Gas Engineer
Messages
159
hi guys,

Had a quick look at job this evening was a ideal logic combi 35. When running for hot water makes a thumping noise. Have cleaned out condensate which defo was blocked up so clearly boiler has never been serviced. Boiler is about 6-7 years old .

Going back Wednesday first thing to have a closer look when I've got abit more time.

Any one come across a similar problem or anything I need have a closer look at.

Customer has also mentioned he's topping pressure up every 2 weeks or so. Will check expansion vessel pressure.

Not used to boiler breakdowns and I'm usually just installing.

Cheers.
 
check the sump as well they like to split around where the front inspection plate is
 
Never heard of a split sump on a combi , they seem to be only heat onlys ...
Is the coni pipe completely clear ?
 
Never heard of a split sump on a combi , they seem to be only heat onlys .
Is the coni pipe completely clear ?
Yeah that was on heat boiler but still ideal.

Cleaned trap out throughly but couldn't see down condensate pipe. Might be worth cutting into it then just coupler it back up.
 
Have heard there was a lot of problems with older ideals (isars) causing similar problems due to faulty electrodes????
 
I would try blowing down it or at least a hose full of water if you suspect anything . I know they have bother with flue seals but it doesnt give a banging noise, have your anyliser on when you draw HW it may show something
 
Sounds like it needs a full service as per manufacturers instructions first.

Then as it sounds like the condensate discharge pipe is blocked somewhere along its length so i would try and flush through or the other way if you can find where it connects to the drain I would disconnect from there and then vac it from that end to pull any residue through.

Also clean sink drain trap & bend if it connects in there.

Prob need a peg for your nose as I have had a few customers that must of emptied god knows what down there & it has stank.

Good luck with it,

Thanks.

Andy.
 
If its blocked and backed up it can cause a kettling/banging noise I have had that problem before with an ideal.
 
If its blocked and backed up it can cause a kettling/banging noise I have had that problem before with an ideal.
if condense was backing up it would gurgle never heard of one banging , how would it cause it to bang ???
 
Sounds like a flow issue though the heat exchanger to me. Is the system water clean or dirty?
 
Status
Not open for further replies.

Similar plumbing topics

Unfortunately most household insurance...
Replies
16
Views
2K
Are you Gas Safe Registered? If not please...
Replies
2
Views
537
W
Hi cjg, thanks for the reply. It was serviced...
Replies
2
Views
1K
Williams25
W
No, decided to go for Viessmann Vitodens 100-W...
Replies
18
Views
4K
im going for another cracked hx.
Replies
9
Views
1K
Back
Top