Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Ideal Logic gas valve fault in the Gas Engineers Forum area at Plumbers Forums

Nico

Gas Engineer
Messages
79
Hi guys came across a strange one today and was wondering if anyone could shed some light cheers.

Had a report of noise coming from boiler. Arrived on site and found when gas valve modulated to minimum rate it the diaphragm would vibrate and sounded like the titanic was arriving through the front door. Changed out the gas valve but has same issue with new gas valve. On minimum rate I was get 21mbar at test point. Check Venturi which was clean and check burner for debris. Tried a fan to see is the gas/air ratio wasn’t mixing correctly but still had same issue.

Anyone had anything similar before?

Cheers for getting back to me
 
hello
 
Hi Shaun,

I am new to this forum and have posted on this public section not knowing there was a private GSR section. How is it you go about being accepted into that section?

Cheers
 
Hi Shaun,

I am new to this forum and have posted on this public section not knowing there was a private GSR section. How is it you go about being accepted into that section?

Cheers

send us your gas safe reg no and i will sort it
 
Copper sulphate on the venture connected to the fan clean it thoroughly and reattach

To be clear I’m a training gas engineer and have done this exact thing to resolve this issue on many ideal logics. If it’s under warrenty ideal come out and replace the whole gas valve
 
Hi guys came across a strange one today and was wondering if anyone could shed some light cheers.

Had a report of noise coming from boiler. Arrived on site and found when gas valve modulated to minimum rate it the diaphragm would vibrate and sounded like the titanic was arriving through the front door. Changed out the gas valve but has same issue with new gas valve. On minimum rate I was get 21mbar at test point. Check Venturi which was clean and check burner for debris. Tried a fan to see is the gas/air ratio wasn’t mixing correctly but still had same issue.

Anyone had anything similar before?

Cheers for getting back to me


-Read my last comment -
 
Copper sulphate on the venture connected to the fan clean it thoroughly and reattach

To be clear I’m a training gas engineer and have done this exact thing to resolve this issue on many ideal logics. If it’s under warrenty ideal come out and replace the whole gas valve

Yep this seams to be a bit of a logic “trait” horrendous noise lol
 
Just to jump in on this. I've had a few now that rumble to flame loss on minimum and it can be a number of different things causing the same problem.
They all lead to getting the gas air mixture exactly right on minimum. There seems to be zero tolerance.
Go for the injector first, clean both inside and out, make it shine again.
Then remove and clean the funnel it attaches too.
Air dust the fan and then the burner.
Pour water into the heat exchanger.
These steps usually cure it.
 
Just to jump in on this. I've had a few now that rumble to flame loss on minimum and it can be a number of different things causing the same problem.
They all lead to getting the gas air mixture exactly right on minimum. There seems to be zero tolerance.
Go for the injector first, clean both inside and out, make it shine again.
Then remove and clean the funnel it attaches too.
Air dust the fan and then the burner.
Pour water into the heat exchanger.
These steps usually cure it.
Cheers mate appreciate the advise will go through this sequence next one I come across a similar issue
 

Similar plumbing topics

Unfortunately most household insurance...
Replies
16
Views
2K
No, decided to go for Viessmann Vitodens 100-W...
Replies
18
Views
4K
Are you Gas Safe Registered? If not please...
Replies
2
Views
536
W
Hi cjg, thanks for the reply. It was serviced...
Replies
2
Views
1K
Williams25
W
Incoming 7degrees, raised by 33 degrees. New...
Replies
14
Views
7K
Back
Top