evening all, just looked at a ideal mini c boiler which was fitted about six years ago, since then has broken down on a few accasions, most recently over last few weeks, over this period the user has kept pressing the reset button to sort out and the boiler did restart everytime, on this occasion the boiler wont fire up at all, goes through all usual sequence upto igniting but then locks out, all manuals say PCB or Gas Pressure, anyone had similar probs? any knowledge would be great, thanks.
 
dont know the boiler, but if the manuals say that, gas pressure is easy to check both standing and operating.
check that, then you know its the pcb
 
Well when it says gas presues what it means is faulty gas valve not opening
When it says pcb it means ignition part of board faulty
check if any gas being release through gas valve just before lock out and that power to valve,if power but no gas fault gas valve sticking,replace,if ok check to see if electrode producing spark ,check leads ok,check electode gap ,adjust clean, if ok pcb then probable ,if you have no power to gas valve fault pre ignition
 
Last edited by a moderator:
seems to be doing everything asked of it upto sparking but locking out after sparking for approx 6 seconds
 
if sparking,fault will be a sticking gas valve,replacement valve required,not an uncommon fault
it is going to lock out as no flame detected
 
could it be the temp probe as i am been informed that last time this happened an engineer hcanged the temp probe and worked again?
 
not if ignition is sparking ,the boiler has passed its checks and ready to light
 
The only thing would add,do not miss the obvious,if boiler been playing up over a few weeks has someone been fiddling and closed manual gas valve under boiler
 
i checked it first off, but like you say can never be sure unless you check these things, people tend to try turning things off without knowing what they are, then forget to put back on!
 
Hmm

What C version is it?

I would not be to hasty in changing the gas valve, before I had checked for the presence of gas pressure, if I was you. Gas valves cost a bomb and if its wrong the customer will not be pleased.
I would also tend to check the integrity of the flame detection unit and electrode.
The air pressure switch and the ignition electrode position.

In point give it a full electrical check, before replacing the gas valve.

But if you have already done this and still no gas coming out of the valve but there is at the inlet, then it seems likely its the gas valve.

The job is time consuming and I would tell the customer that, then take my time testing.

Don't forget if you sent a telly in for repair, you would expect to wait, a modern boiler can be a complex bit of kit and can take just as long.

And don't forget for most appliances they would be repaired on a work bench with loads of test gear. You are attempting to do the same to an appliance stuck on a wall or in a cupboard, which usually you can't reach properly.

Good fortune! :) :)
 
Status
Not open for further replies.

Similar plumbing topics

More than fine then in 11/5 tube should be...
Replies
3
Views
674
Just do the same action again. Pot at Mac...
Replies
9
Views
2K
I have connected the secondary pump to a wifi...
Replies
9
Views
2K
H
Hi there, thanks for your time to look at this...
Replies
0
Views
911
HRP123
H
Your gas rate is your big one to check. Well...
Replies
9
Views
213
Back
Top